Why?? It's a 1.2 M 3/8'' rod with around 20cm stuck out of the ground, with a numbty Earth box sat on top of it!! And installed in just about the worst position you could wish for!!! Where all the original building rubble will be, not that would have been a problem, the dammed rod doesn't go down deep enough to hit any rubble!!! That rod will be about as stable as an alcoholic on a Friday night binge!! lol!!!
hope this helpsDo you always try and put your bond clamp inside the property (if possible) as opposed to outside? (obviously in my case it has to be outside). Bonding ideally should be inside the property after the meter (within 600mm) and before any branch pipework. Though it can be bonded outside if required.
Is this earth clamp ok to use for outside use:
http://www.******************/Images/Products/size_3/EC14.JPG
Or should it be a specific type due to the elements?
This clamp is only suitable for internal use, you need the EC15 or EC16 clamp for use outside.
And should the hole in the wall for the main bond be a seperate hole in the wall from the earth cable that enters from the earth rod? No
Edit: With regards to the 0.5ohm or less reading indicating its reliably connected to earth - where can I found that in the BGB or OSG?
This is not ,I think, in BGB or OSG, it is in GN3, the value is 0.05 ohm not 0.5ohm. This is a general rule of thumb to see if there is supplementary bonding in place and it can be considered to be in place if the continuity value is less than 0.05 ohm.