Probably a basic question

In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal

What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
 
Probably a basic question

In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal

What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
The earthed metal would surely be bonded if extraneous, no?
 
Probably a basic question

In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal

What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
It's either extraneous or it isn't.
Have you measured it ?
 
Probably a basic question

In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal

What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
By earthed metal, I assume you mean metal that is connected to the MET?

For example: plastic incoming supply pipework, metal pipework to boiler, boiler connected to MET via CPC.

The metal pipework is not an extraneous part, so not introducing an extraneous potential. It is however connected to the MET via the boiler and CPC. All that bonding would do is connect it to the MET again, achieving the same thing.
 
By earthed metal, I assume you mean metal that is connected to the MET?

For example: plastic incoming supply pipework, metal pipework to boiler, boiler connected to MET via CPC.

The metal pipework is not an extraneous part, so not introducing an extraneous potential. It is however connected to the MET via the boiler and CPC. All that bonding would do is connect it to the MET again, achieving the same thing

Will it achieve the same result in the event of a fault?

The CPC connected to boiler or a main vond connected to the metalwork that's not extraneous
 
I always found this article helpful, with regards cable tray;

 
Probably a basic question

In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal

What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
If metalwork is directly connected to earthed metal, what would be the point?
Am I missing something, here?
 
Will it achieve the same result in the event of a fault?

The CPC connected to boiler or a main vond connected to the metalwork that's not extraneous
I believe so. Here's how I see it:

When a direct short occurs between L and earthed metalwork, a circuit is completed via the CPC, back to the MET, and back to the transformer via whatever earthing system is in place, and possibly through bonded extraneous parts.

Like any circuit, there will be voltage drop throughout the fault loop, with the highest potential for accessible metalwork being at the site of the fault, and the lowest being at the MET.

In my example above, the metal pipework is already connected to the MET via the boiler CPC, and is not taking a potential from anywhere else (it's not an extraneous part), so it can't be at a lower potential than the MET. Connecting the pipework back to the MET with bonding would not bring the potential of the pipework any higher than it already is.
 
I'm just presuming 'earthed metal' to be part of the earthing system. If something needs bonding, it's not.
I don't really know if they meant earthed as in to the Met or Earthed as in Terra Firma, which is why I asked the question.
 
It's either extraneous or it isn't.
Have you measured it ?
Not extraneous
I'm just trying to understand the shock risk between the pipework that is earthed by the boiler and another piece of exposed metal if it becomes live temporarily

So you've got 1 hand on the pipework and another on say a piece of live exposed metal
 
So you've got 1 hand on the pipework and another on say a piece of live exposed metal
If you have one hand on a live piece of metal and another on a pipe that's earthed via the boiler, then you're going to get one of the worst types of shock you can have, one that's across your chest.
 

Reply to Main bonding questions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
54
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top