Is it ok to clamp 10mm earth cable to the gas pipe then to the water pipe and then to the Installation earthing terminal or do the have to be sepatete cables, the cable runs are about 3m.

Many thanks in advance
Mark
 
Is there a metallic waste pipe?

Is the water supply taken from a different source than from the main water supply?

Is there any extraneous conductive parts on the sink?

Does the utility room also contain a bath or shower?

Just a quick question, why are you asking if the utility room also contains a bath or a shower?

Thanks.
 
John if they are extraneous conductive parts then yes they should be bonded, reg 4113.1.2 (iii).

Not sure why you want to bond them on exit mate, but certainly on entry.

As for the 50mm SWA well normal SWA will give you copper eqiv of about 32mm and XPLE dead on the 25mm required in reg 544.1.1

Had to edit that of course 50mm 2 core XPLE would only be about 22mm copper eqiv and therefore not suitable

It is my. Understanding when swa is used as a bonding conductor we work out its copper equivelent which for a 50mm 2core xple works out at about 8.5mm when its used as an earthing conductor it is 22mm .
 
hi thanks for the chart

I=P/u but that chart is for the use with armouring as a CPC not a bonding conductor, as a bonding conductor the copper equivelent is less as that shown on this chart chart on the forum, i think it is to do withy the resitivity of the steel etc a bonding conductor the csa must be 8 times the value of the Copper equivelent thesfore a 10mmsq copper bond requirews the armouring to be 80mm steel CSA, see the top of page 42 of GN8 as this is where this is stated !

if you have access to it the electrical saftey council techincal manual A 57-21 goes into the subject in some depth
 
Last edited by a moderator:
I've been reading the regs book and come across reg 411.3.1.2 which starts "In each installation main protective bonding conductors (note the s on the end indicating more than 1) complying with chapter 54......." you can also look at the pictures in the OSG which show seperate bonding conductors.
Doesn't say you can't use 1 continuous cable though.

Interpret as you will. Wish it was all written so there was no ambiguity!
 
main protective bonding conductor !

honest mate i dont think many people realise this, we in the past have used armouring on cables as a main bonding conductor from sub mains before thinking it was sufficant and it has not been the case,
 

Reply to main bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
997
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
779
loz2754
L
I like your way of thinking.
Replies
6
Views
723
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top