HI all,

usually take tails form a MEB box to consumer unit no matter what the length as long as i can get the 50mm depth, builder has told me he wants it in SWA, ive told him its pretty much impossible to terminate it right if i use SWA also i run up the cavity with the tails and there is no way i can get SWA up there so will have to run inside up the wall which i hate doing, what do you guys do if using SWA??

Cheers
Grand
 
Are you talking concentric or split concentric because I have often wondered as originally it was deemed acceptable.

I mean split concentric, the requirement for buried cables is that they have earthed armour or sheath etc. Split concentric doesn't satisfy this.

I don't know if it was ever deemed compliant for burial in a wall without RCD since that rule came in.
 
its not particularly recent, But if I was to do the job today I probably wouldn't change it for metal and would record it as a departure on the EIC.
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly
 
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly

A departure is a non compliance, if it complied then it wouldn't be a departure.

At the time there was no suitable metal option.
Now I am still not aware of a suitable metal option, bearing in mind it is in a meter box so steel is not suitable because it will rust.
The KMF is made of a Bakelite type plastic which to the best of my knowledge is not readily combustible in the way that the soft plastic used for CUs is.
It is located outside of the building and presents no greater risk than the other plastic equipment installed in there (meter, cutout, Henley block)
 
A departure is a non compliance, if it complied then it wouldn't be a departure.

At the time there was no suitable metal option.
Now I am still not aware of a suitable metal option, bearing in mind it is in a meter box so steel is not suitable because it will rust.
The KMF is made of a Bakelite type plastic which to the best of my knowledge is not readily combustible in the way that the soft plastic used for CUs is.
It is located outside of the building and presents no greater risk than the other plastic equipment installed in there (meter, cutout, Henley block)
To depart is to install or use something that is no less safe than full compliance with bs 7671 so if bs7671 calls for non combustible enclosure on a consumer unit or similar switch gear assemblies and you don't adhere to the regulations then it's a non compliance to me and not a departure
 
Personally I feel the KMF is the wrong choice for the job in the above pics due to it having to be installed upside down as the load side is at the top..I would of opted for something different or done the job differently if nothing else would fit in the cab.

It only had to be installed upside down because I'd made off the cable and fitted the KMF the right way up before I realised my mistake.
Had I paid a bit more attention it would have been done differently the KMF would be the right way up.
 
Why not metal ? You could gland straight into it
Also explain how it's a departure and not a non compliance?
It's not a consumer unit but I'd put it as a similar switch gear assembly
If you decide to record a departure then the level of safety should not be less than obtained by compliance with the Regulations. It can be difficult to prove such things. DSs explanation in #24 does have validity that the enclosure is more likely to char than ignite but whether its level of safety is less could be debated. The only thing I would comment on if I undertook an EICR is that it is upside down :D
 
To depart is to install or use something that is no less safe than full compliance with bs 7671 so if bs7671 calls for non combustible enclosure on a consumer unit or similar switch gear assemblies and you don't adhere to the regulations then it's a non compliance to me.

Yes well as the designer I deem this departure to be no less safe than compliance with that particular regulation.
 
If you decide to record a departure then the level of safety should not be less than obtained by compliance with the Regulations. It can be difficult to prove such things. DSs explanation in #24 does have validity that the enclosure is more likely to char than ignite but whether its level of safety is less could be debated. The only thing I would comment on if I undertook an EICR is that it is upside down :D

I'd question it being upside down too, I wasn't very happy with that when I fitted it but I'd dug myself into a hole and had to get out of it.

This has got me wondering whether GRP would be considered non-combustible
 

Reply to Mains box to Consumer unit SWA or tails? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
705

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
691
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top