The appendix then points you back to Reg 526.3 and in that reg the ashley box does not comply to any of the sections. It does not use screws granted but it also does not use compression by a tool like a crimper.

I have discussed this and the nearest that I can be persuaded is by the use of regulation 120.4 new inventions, but I'll reserve judgement on them until the amendment comes out in July, and see if these type of boxes are included in it.
 
According to the Hagar website, the Ashley JB's are 17th Edition compliant, (they do use the term "equipment" in the brochure) see:
Junction Boxes & Ceiling Accessories Hager

The last page has a junction box selection chart and it clearly shows the maintenance free jb's J803 and J804 as "suitable for use in inaccessible locations"

Surely Hagar couldn't make these claims if they aren't compliant.

It'll be interesting to see what the new regs have in store.
 
So called maintenance free terminals are not at present accepted as such by BS7671.
526.3 lists the types of joint that are accepted as being maintenance free.
As far as I'm aware they meet the requirements of BS EN 60670 which is the standard for enclosures. In other words, the terminals do not have to be in a separate enclosure, because they are deemed to be one.
As such they meet the requirements of the 17th edition, just as do JBs adaptable boxes and other enclosures.
Meeting the requirements to be an enclosure, does not then mean they are acceptable as a maintenance free joint under the 17th edition.
Departures from the Regulations are allowed, if they afford the same degree of safety as would be achieved by compliance with the Regulations.
If you have evidence from the manufacturer's that these 'maintenance free' terminals are as safe as other acceptable forms of maintenance free joints, then they can be used, as long as their use is detailed in the section for departures on whichever Certificate is being used.
 
I'm still confused with the conflicting views.

The PDF on Hagar site clearly states that the J803 and J804 are maintenance free and as such can be used in inaccessible areas. Here follows a direct quote from the pdf:

"The Maintenance Free junction box provides a secure and maintenance free means of
connecting fixed wiring in any indoor application, whether it be under floor situations, between
ground and first floor in houses, or where jointing of cables is used to aid rewiring.
BS 7671 (Wiring Regulations) recognises equipment complying with an appropriate British
Standard without further qualification. Therefore, a junction box marked MF is identified as a
maintenance free accessory, which does not require further inspection, testing or maintenance
after installation in a circuit."

As mentioned in my earlier post, surely Hagar can't just make claims like this up. If these JB's are not compliant with 17th Ed many sparks who have used them have may have done so incorrectly and it could be argued need to do remedial work to rectify. If that's the case is it reasonable that Hagar pay for additional works?
 
Nothing there actually states that it can be used as an inaccessible joint?
It states that it can be used in places where JBs would normally be used.
It then states that it is recognised by BS7671, as are JBs.
Then states that it is identified as a maintenance free accessory.
Nowhere does it actually state that it meets the requirements of BS7671 for an inaccessible joint.
 
I'm with Spin here, it does not at the moment comply with the regs for a non accessible joint, the literature stops short at saying there is no need for it to be inaccessible, but that it does not need maintenance, inspection and testing after installation.

They maybe correct and that after fitting it there is no need to check it again, but until it complies to reg 526.3 IMO I would not use it as an inaccessible joint.
 
Interesting how this information can be interpreted. I am going to email Hagar and try to get a definitive answer to this. Don't know if and when they will reply but I'll report back if they do.

Lee
 
I like the advise of Spinlondon and Malcolm

Further to that and speaking with out ever having seen these joints,so from total ignorance :eek:

I have yet to have faith in any push fit joint that I have seen, to even consider for a moment using them where access could not be absolutely assured :eek:


So whether they are permitted or no,I would always advise a proper connection :cool:
 

Reply to Maintainance free JB's e.g. Ashley J803 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
814
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
988

Similar threads

How many and what type of cables do you want to join, Chocbox is the last thing I would use.
Replies
3
Views
698
Hello all easy cert users, ive been using easy cert since 2001 with no yearly subscription. and also found other people looking for older versions...
Replies
0
Views
156

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top