Another option that you might consider is splitting the meter tails via henly blocks, then feeding 3 or more switched fuses with bs 1361 II 40 amp fuses, that in turn feed 4 way boards via 10 mm tails, the smaller feeders to the boards will lower the psc to a value more in spec with protection with bs/en 60898.
It might look like something out of the late 70s with 3 or more switched fuses and boards, but when economy favours over appearance, then compliance is paramount.
Just out of interest what psc are you getting at the first outlet on any circuit when you perform a loop test?