Wriggling is exactly what you do on this subject! lol

Even the most trivial of questions pop up on TT systems and every time you've gotta stick your two cents in with regards to 200 ohms being rubbish. Every time without fail! You bite, get reeled in and then get thrown back into the pond for the next chump to throw you a 'TT' line :D

The most straight forward response to the OP's question would be something like; "200 ohms is the max recommended Ra by definition of the regulations, your 38 ohms is fine on a domestic install, stick an up front type-s in on the tails and RCD protect the existing board with one or two 30mA jobbies. If the customer doesn't like the idea, walk away."

That is all the OP needed to know, your thoughts on whether or not you think 200 ohms is a good value to achieve are not really relevant as he already has one of your magical Ra values at 40 ohms. It also doesn't answer his question.

I'm not gonna get into another '20 ohms or 200 ohms' debate with you, we all know and I hope respect our differing views on the matter. I'm purely pointing out how I giggle when I read a TT related thread knowing any minute you'll pop your head round the door with "Argh! 200 ohms this! 200 ohms that!" haha!
 
Sorry but that's not wriggling, Facts are facts and 200 ohms is just a ridiculous and laughable farce at best. But you're right i will keep stating that fact, in the hope that those that know no better will realise that fact. The chumps here, are those that just accept and or try to defend the ridiculous!!
 
Last edited by a moderator:
What? Like 20 ohms being better than 200 ohms? :D

*Nope! Zip it Mr Skelton, you can't be seen biting the bait you're casting out!* haha!

Well i damn well know what i would prefer to see between the two, even if you dont!!

Cast away, makes no difference to me one way or the other!! lol!!
 
Come on E54 lighten up a little

Looking at the 15th edition the max RA for VOELCBs was 500 ohms (including the rod and earthing conductor), the 16th just gives the usual Zs Idn=< 50V for RCDs and this will comply, it doesn't state a max although the 16th OSG recommends that it should not exceed 220 ohms , the 17th edition actually lowered the RA to 200 ohms max.
 
Last edited:
How about this:
Will a RCD work even without a main earth!

I also like the new range of Eaton RCBO's which come without an earth flylead, much neater in the board. Took them long enough to realise that.
 
Don't really want to add to/become embroiled in the usual argument that kicks off about TT systems, but the Regs do not say 200 ohms is a max. As D Skelton says the Regs just say anything over 200 ohms can be 'unstable'. I doubt anyone would disagree with this fact?
 
No Richy not disagreeing at all,

in my post above yours these are the max recommended, just I omitted that for clarity, we all know this already.

The important point is the formulae given in all editions, where the rod should not be able rise above 50V, and in some cases 25V, and it should be matched to the protective device.

The 16th regs are a little unclear, as it gives the Zs formula also in the above post, and this implies that so long as the Zs complies at the end of the final circuit/s then the rod also complies, it is only in the 16th OSG that mentions 220 ohms, but unlike the 17th does not give any reason why (ie. unstable) nor does it give a reg number, because there isn't one.
 
We know what it say's, but i'll guarantee you, that virtually every poster that comes on this and other forums, that isn't knowledgeable on TT systems, take that figure in BS 7671 as being the stated maximum and that's what they inevitably will work too!! ...And why i always Poo it off!! lol!!

The whole section on TT earthing needs a thorough sorting out and a bit more guidance wouldn't go amiss either!!

I'm going home (Cyprus) for Xmas this year, and while home, i'll be checking my own TT system. Earlier this year (early summer) it was around 0.93 ohms which has been steadily dropping year on year from around 4'ish ohms.

Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year.

It's surprising what can be achieved when you know what you're doing!! lol!!
 
Spark 68 - comment wasn't directed specifically at you matey.

Incidentally my DNO manager recently mentioned '200 ohms' when we were taking about TT systems so I don't know if the figure comes from ESQCR?
 
How about this:
Will a RCD work even without a main earth!

In a word, no. Fault current needs a path to earth for an RCD to operate. If that path is through you then yeah, it will operate if your bodily resistance combined with the resistance of whatever you happen to be standing on is low enough to allow more than the rated current of the RCD to flow. That said, the requirements of fault protection will not be met if a fault can occur leaving an exposed conductive part live and ready for you to become the earth path!

Im assuming that I'm providing an answer to a genuine and not a rhetorical question :D
 
We know what it say's, but i'll guarantee you, that virtually every poster that comes on this and other forums, that isn't knowledgeable on TT systems, take that figure in BS 7671 as being the stated maximum and that's what they inevitably will work too!! ...And why i always Poo it off!! lol!!

The whole section on TT earthing needs a thorough sorting out and a bit more guidance wouldn't go amiss either!!

I'm going home (Cyprus) for Xmas this year, and while home, i'll be checking my own TT system. Earlier this year (early summer) it was around 0.93 ohms which has been steadily dropping year on year from around 4'ish ohms.

Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year.

It's surprising what can be achieved when you know what you're doing!! lol!!

So, is your nightmare an illiterate Electrical Trainee, Part P 'registered' trying to 'do' a TT install ;)

Please give people some credit - the wording is not that technical. There's a big difference between 'over 200 ohms can be unstable' and '200 ohms is the maximum permissible value'?
 
In a word, no. Fault current needs a path to earth for an RCD to operate. If that path is through you then yeah, it will operate if your bodily resistance combined with the resistance of whatever you happen to be standing on is low enough to allow more than the rated current of the RCD to flow. That said, the requirements of fault protection will not be met if a fault can occur leaving an exposed conductive part live and ready for you to become the earth path!

Im assuming that I'm providing an answer to a genuine and not a rhetorical question :D

I said will it work, and you have said yes! In saving your life!
 

Reply to Max Ze for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978