RCD on a TT must operate within 200mSec. this is achieved by a Zs value of <1667 (30mA RCD).
Of course, my bad.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Max Ze for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
RCD on a TT must operate within 200mSec. this is achieved by a Zs value of <1667 (30mA RCD).
Hope this isn't a stupid question,
Given what has already been discussed regarding TT systems, how is it possible to get acceptable Zs readings which will comply with table 2D OSG.
When i first came into this industry the recognised max for a Roded earth electrode was 10 ohms, FACT!! Never saw one anything like at that value mind, all were generally in the lower single figures.
So now were being sold a complete crock crap that 200 ohms is the max figure to aim for!! If for no other reason, a 200 ohm earth electrode, or anything remotely like it will ''NOT'' provide a stable TT system.
I got a bite! A big one! C'mon lads, get the landing net out ready, this one's gonna be a wriggler!
It shouldn't cost a penny, the old regional boards used to convert TT systems for nothing, in fact that was one of the main reasons the electricity boards invested so much cash into PME'ing overhead and later failing underground cables, to provide homes and businesses with a stable means of earthing!!
Seems now the private DNO's think it's fine to charge for this once totally free service. But seeing as it takes about 2 to 3 min's to convert (depending on the service head) it shouldn't cost an arm and
recently quoted 140-160 by the DNO - in the end after tea and biscuits, no charge. And a free isolator. Yippee.
When i first came into this industry the recognised max for a Roded earth electrode was 10 ohms, FACT!! Never saw one anything like at that value mind, all were generally in the lower single figures.
So now were being sold a complete crock crap that 200 ohms is the max figure to aim for!! If for no other reason, a 200 ohm earth electrode, or anything remotely like it will ''NOT'' provide a stable TT system.
With respect, how big were the rods & how close to the ss would that have to be.
I never seem to see much below 30 ohms.
Regards