Max Ze for TT system
If you touched a live cable and you was not earthed, you would not get a shock as there is no path to earth. If you make a path to earth then rcd opens simple.
Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year!
Bearing in mind that we are talking about commercial/industrial applications here and not your average domestic house. I have never left a commercial/agricultural TT system with more than half an ohm for an Ra value. The lowest Ra value I ever reached was a steady 0.3 ohms.
Domestic wise however, I'd be happy with a couple of 4 footers, an Ra value of 200 ohms and a type-s up front. Last year I happily left a domestic with an Ra value of around 250 ohms even after punching in 8 foot of copper into solid chalk. I went back every month for six months in a row to check its stability and the value hadn't budged.
But the whole point is that the system should disconnect before you can touch what is live! If there is no earth you are left merely hoping that the path to earth that you provide to the fault current is higher than the rating of the RCD!
What if you clamped hold of a live part protected by a 30mA RCD but your resistance meant that a fault current of only 25mA flowed? Give it a few seconds and then you're dead!
Just to clarify,
the max recommended values I gave earlier were for run of the mill and domestic type circuits and not for the more specialised installations.
Just to clarify,
We gathered that :) Any spark worth his weight will know that it isn't always feasible to provide a TT system that delivers TN values to your average domestic installation. It's when you start getting into systems of 200A and over that unless you want to start spending a few thousand on an adjustable 'B' type RCCB, it's best just to provide TN values to protect your metal switchgear.
Final answer?
What about class 2 lighting circuits that have no earth?
Yes final answer lol
That is entirely irrelevant. You're relying on a different protective measure entirely, one where RCD's are useless.
Edit: let me rephrase that. The protective measure of using double or reinforced insulation cannot be applied in a domestic setting. Where an existing lighting circuit has no earth and it has not been rewired then you are correct, you are relying on both class 2 fittings and an RCD for addtional protection of the cables buried in walls. This doesn't change my answer though. Bash a nail into that cable and nick the line conductor only, touching that nail doesn't guarantee disconnection :)
If you really want to be pedantic Mr E then an RCD just provides differential protection, or an imbalance between the current flow between (for simplicities sake) output terminals and relies on whatever leaves one terminal returning on the other.
In the context of BS7671 (EEBADS/ADS) then this usually utilises the earthing system to work, but it doesn't actually need an earth to work, just merely the conditions to create an imbalance will trip it, look at the way the test button works.
MBEINST,
Guest 004,