hi can anyone help I have a 3 phase bussbar protected by BS 88-2 fuses rated at 630 amps I need to know what is the max Zs allowed for this ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Max Zs for Bs88-2 630amp fuse in the Talk Electrician area at ElectriciansForums.net
Reading it, the Lawson ref lists 240V and this may be 230V, if that makes any sense?Cooper Bussmann list it as 0.054 ohms for a 630A BS88 HRC fuse
Accurately measure some 1.5 singles to say 0.10 ohm. Take a Zs at the busbar with meter leads only then take another reading with your known resistance in series with one of the meter leads and then deduct the 0.10 ohm and see if it differs from the original reading. This often works if you are very close to the transformer.And you think the reading is not realistic because of the transformer ? How would you recommend putting a resistance on the circuit bearing in mind it's an open occupied hotel ! Sorry I've never come across this problem and not really tested bussbar