But we have to assume competency on the part of the installer or the entire content of BS7671:2008 is pointless.

The 200 Ohm figure for earth electrode Ra is a figure that allows for degradation of soil resistivity from freezing/drying etc. but as i've said many times, I'd take an Ra of 500 Ohms on a deeply driven rod rather than 200 Ohms on a 1.5 Metre rod because on the first good drought or frost, my deeply driven rod will be almost immune.

I accept that there are installers that are not competent, I read their PIR's every day but we can't alter the regulations to suit the lowest common denominator.

Been talking to a couple of old friends on the subject,
Respected and very competant electrical engineers I might add.
Enjoyed our pint, and one said.
If you were driving down a road where the speed limit was 60 mph. You wouldnt just keep to that speed because it says so.
You would use your own judgement as a competant driver to negotiate bends in the roads ect at much lower speeds than stated, and for reasons of safety.
When put like that, who am I to argue.
 
Been talking to a couple of old friends on the subject,
Respected and very competant electrical engineers I might add.
Enjoyed our pint, and one said.
If you were driving down a road where the speed limit was 60 mph. You wouldnt just keep to that speed because it says so.
You would use your own judgement as a competant driver to negotiate bends in the roads ect at much lower speeds than stated, and for reasons of safety.
When put like that, who am I to argue.

If I'd have been more 'skilled with the pen' I'd have used that analogy, perfect!
 
if I were to be pedantic, as a lot of people on here are, by saying they put 1667 because that is what it says ,then they are wrong the actual figure is 1666.67 so they should be filling in 1666 if they are rounding it off ( round down not up, it's the pessimistic nature of all regulations especially IEE ones)

50 (volts) / 30 (milliamps) = 1666.67
 
Last edited by a moderator:
While I can't dispute your maths, the 1667 Ohm value is taken from Table 41.5 in BS7671:2008
 
no mate. roundeedd off it's 1667 to the nearest whole number. if i remember correctly the last significant figure of 1666 was the great fire of london. now that was a disaster, but at least it killed off the plague. let's hope this figure related to our work don't kill off anyone.
 
no mate. roundeedd off it's 1667 to the nearest whole number. if i remember correctly the last significant figure of 1666 was the great fire of london. now that was a disaster, but at least it killed off the plague. let's hope this figure related to our work don't kill off anyone.


a few ohms were lost in that one
 
I only started this because of his Arsenal trophy joke this morning!
 
Some say that he wrote the 1st edition on the back of his JPS packet.......and that if it wasnt for him the RCD would be a myth.......all we know is he's called.......what ever we feel like at the time!!!!;):p:p:D:cool:
 
Some say that he wrote the 1st edition on the back of his JPS packet.......and that if it wasnt for him the RCD would be a myth.......all we know is he's called.......what ever we feel like at the time!!!!;):p:p:D:cool:

And he's the oldest spark (ten second Clarkson pause) in the world.
 

Reply to Max Zs readings where circuits are protected by 30ma RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
686
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
682
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top