Hi I've just moved testers from fluke to megger 1553, just wondering if the socket test lead measures the R1 & Rn reading when testing a ring main. The R1 + R2 reads ok just wondering if I need to purchase a Kewtech R2 mains adapter Thanks
 
Hi Simon,

The mains test lead from the MFT1553 cannot beused for measuring R1+Rn but you can use the SIA10 mains test lead or a mainsadaptor as you mentioned.
 
Not sure if this is of any help but I have just go hold of a Megger 1730 and was wondering the same thing. I was informed by Megger to use the lead with the plug attachment and as this comes with 3 separate leads on the end. So you only plug the leads you need into the meter.
 
Not sure if this is of any help but I have just go hold of a Megger 1730 and was wondering the same thing. I was informed by Megger to use the lead with the plug attachment and as this comes with 3 separate leads on the end. So you only plug the leads you need into the meter.

Thats right th 1700 series has that lead where as the 1500 series didn't. I bought the lead with the 3 separate plugs on as an extra afterwards.
 

Reply to Megger socket test lead in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
388
There is a lock on it, press the test button down and press the lock button, the symbol will appear on the screen in the middle right hand side...
Replies
5
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top