rattlehead85

Would like a bit of advice on how others have tackled this.
Got a situation where we have a TN-C-S supply to a house with a 6mm 2core swa feeding a detached garage using a T.T. Earthing arrangement with a service water pipe within the garage which has a 10mm bond to it. My question is the client has provided a new Metal clad Rcd 30mA front line board to install in the garage, what would be the best and most effective way of separating the earthed armour of the swa feeding the garage from the earthing system employed to the garage itself T.T. [emoji106]
 
Would like a bit of advice on how others have tackled this.
Got a situation where we have a TN-C-S supply to a house with a 6mm 2core swa feeding a detached garage using a T.T. Earthing arrangement with a service water pipe within the garage which has a 10mm bond to it. My question is the client has provided a new Metal clad Rcd 30mA front line board to install in the garage, what would be the best and most effective way of separating the earthed armour of the swa feeding the garage from the earthing system employed to the garage itself T.T. [emoji106]

Sorry if I'm being dim here (only a trainee), but wouldn't a PVC adaptable box solve this problem? Gland SWA to adaptable box to separate the two earthing arrangements, put the adaptable box just below your metal DB. Either butt the two up to each other (and use 20mm PVC grommets to prevent cable damage) for the tails, or a conduit coupler and a couple of bushes for a slightly neater job.

Or have I missed summat? :)
 
Last edited:
Sorry if I'm being dim here (only a trainee), but wouldn't a PVC adaptable box solve this problem? Gland SWA to adaptable box to separate the two earthing arrangements, put the adaptable box just below your metal DB. Either butt the two up to each other (and use 20mm PVC grommets to prevent cable damage) for the tails, or a conduit coupler and a couple of bushes for a slightly neater job.

Or have I missed summat? :)

You could do that, or an insulated gland plate might be possible, but you have to be sure you cannot simultaneously touch the exposed conductive parts of two different earthing systems, as a potential difference could occur say from a PME earthed metal gland and the TT earthed metal CU/DB.

Another problem is that the TT earth fault loop impedance may be too high to reliably disconnect the upstream OCPD prior to the metal clad board, leaving a possibility during a fault of the metal CU becoming live as well as the TT CPCs, there are ways around this such as insulated (effectively class 2 cableways for the main tails), an upfront 100mA (or whatever is suitable for the particular RA) RCD to protect the tails prior to the CU, careful insulated glanding etc.
 
You could do that, or an insulated gland plate might be possible, but you have to be sure you cannot simultaneously touch the exposed conductive parts of two different earthing systems, as a potential difference could occur say from a PME earthed metal gland and the TT earthed metal CU/DB.

Another problem is that the TT earth fault loop impedance may be too high to reliably disconnect the upstream OCPD prior to the metal clad board, leaving a possibility during a fault of the metal CU becoming live as well as the TT CPCs, there are ways around this such as insulated (effectively class 2 cableways for the main tails), an upfront 100mA (or whatever is suitable for the particular RA) RCD to protect the tails prior to the CU, careful insulated glanding etc.

Thank you :) Knew I'd missed summat! Cheers.
 

Reply to Metal CU in garage T.T system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top