Got a situation where we have a TN-C-S supply to a house with a 6mm 2core swa feeding a detached garage using a T.T. Earthing arrangement with a service water pipe within the garage which has a 10mm bond to it. My question is the client has provided a new Metal clad Rcd 30mA front line board to install in the garage, what would be the best and most effective way of separating the earthed armour of the swa feeding the garage from the earthing system employed to the garage itself T.T. [emoji106]
 
Is the 10mm bond taken back to the house then? Why are you Making the garage a TT system?

No the T.T system and earthing to the garage was already in place as was the water pipe bond. The problem was the swa running into the garage was terminated into an old plastic smashed C.U with no gland used, the cable was just poked through a knock out. The client went and bought the metal board against my advice so now left with adequately terminating the supply cable whilst keeping the earthing separated and not exposed to simultaneous touch.
 
Ideally the TT CU should be class 2, another way is to add an upfront 100mA RCD before the metal CU and obviously the armourings not connected at the TT side, alternatively a suitable insulated gland as Archy pointed out above ^^^ might be enough.
 
No the T.T system and earthing to the garage was already in place as was the water pipe bond. The problem was the swa running into the garage was terminated into an old plastic smashed C.U with no gland used, the cable was just poked through a knock out. The client went and bought the metal board against my advice so now left with adequately terminating the supply cable whilst keeping the earthing separated and not exposed to simultaneous touch.

why don't you drop the TT Earth and gland the SWA at both ends and use the SWA as the earth if the water bond in the garage is already connected back the MET in the house.
 
[ElectriciansForums.net] Metal CU in garage T.T system
 
why don't you drop the TT Earth and gland the SWA at both ends and use the SWA as the earth if the water bond in the garage is already connected back the MET in the house.

No the water is bonded back to the earthing within the garage. Cant see how you could drop the T.T. and connect the swa at both ends the water bond would then not comply size wise as the supply to the garage is only 2 core the armour on the 6mm aint big enough to carry the water bond back to source.
 
Because the sub-main is only 6mm, and inadequate for MPB purposes, 10mm minimum required for TNC-S

Yes I totally understand this especially after that other never ending thread lol.

Oops I took it as the water in the garage was bonded to the MET and the garage sub board had been made a TT system. Silly me lol
 

Reply to Metal CU in garage T.T system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top