R

rattlehead85

Would like a bit of advice on how others have tackled this.
Got a situation where we have a TN-C-S supply to a house with a 6mm 2core swa feeding a detached garage using a T.T. Earthing arrangement with a service water pipe within the garage which has a 10mm bond to it. My question is the client has provided a new Metal clad Rcd 30mA front line board to install in the garage, what would be the best and most effective way of separating the earthed armour of the swa feeding the garage from the earthing system employed to the garage itself T.T. [emoji106]
 
No the water is bonded back to the earthing within the garage. Cant see how you could drop the T.T. and connect the swa at both ends the water bond would then not comply size wise as the supply to the garage is only 2 core the armour on the 6mm aint big enough to carry the water bond back to source.

Sorry bud read it wrong and took it as the bond was connected to the MET and the garage sub board had been made a TT system.

IMO the easiest way would be to get the customer to go and exchange the board for a plastic one.
 
Because earthing and bonding are 2 different concepts. The resistivity of steel is 8x that of copper therefore you'd need the armour of the 6mm to be 80mm2 for it to comply as 10mm2 is required for a copper cable on a TN-C-S


Ah ok so you can if its a big enough cable? I've got a pdf here somewhere with the CSA of the steel on.
 
So what happens next year then if all this non combustible malarki means we end up going down the ferrous route??

Hagar for one do a class 2 conversion kit for their metal clad boards for TT, Niccy say you can use an insulated gland and careful routing of the tails, or an upfront 100mA RCD or whatever where the EFLI is too high to disconnect the supply OCPD on TT.
 
Sorry bud read it wrong and took it as the bond was connected to the MET and the garage sub board had been made a TT system.

IMO the easiest way would be to get the customer to go and exchange the board for a plastic one.

What!!!!!.....about the fire hazard. Are you not working to Am3 :eek:mg_smile:... :icon12:
 

Reply to Metal CU in garage T.T system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top