R

rattlehead85

Would like a bit of advice on how others have tackled this.
Got a situation where we have a TN-C-S supply to a house with a 6mm 2core swa feeding a detached garage using a T.T. Earthing arrangement with a service water pipe within the garage which has a 10mm bond to it. My question is the client has provided a new Metal clad Rcd 30mA front line board to install in the garage, what would be the best and most effective way of separating the earthed armour of the swa feeding the garage from the earthing system employed to the garage itself T.T. [emoji106]
 
I gave up with most of those types of tables after that last thread lol :) , we used to use the division of 8, but after looking in GN8 where it suggests 8.5 I might have to revise this again, luckily I used an extra core where there was doubt, erring on the side of caution.

Spark68, sorry I don't know your name, but are you suggesting then just divide it by 8.5 as per GN8
 
Spark68, sorry I don't know your name, but are you suggesting then just divide it by 8.5 as per GN8

I am going to re-think and revise this, as I think probably GN8 might be on the over cautious side, I am going to have a closer look at some cable data where the SWA can be used as the CPC, and try to find some sensible calculations, but yes in GN8 it says that steel is 8.5 times less conductive than copper, more research is needed I think.
 
Uksparks I know it's a bit of topic but if using the swa as the cpc ( not for bonding) use table 54.7 in the BYB page 166 Then you just have to compare it to the manufactures data for the typical CSA of the swa.
 
What you're all reading here is for CPC compliance only, NOT when (in this case steel wire armouring) is to also comply for MPB, especially where the supply is PME. In this case the CSA of the steel wire needs to be around 80mm to be equivalent to a 10mm copper cable.... It's that simple!!
 
That's hope Geoff doesn't see this thread other wise we are in this for the long haul haha :icon12:

Oddly enough lol OT for this subject , I was looking through GN8 at the hi-integrity earthing section, and you can use the armourings for the second CPC, conditions permitting of course :) it actually states this is allowed for that application. Bloody regs! they just make it up as they go along lol :ack2:
 
Yes as we have identified some posts back the armouring can be used as a cpc upto about 95mm2 for swa however not for bonding purposes unless you can ascertain the armouring is correctly sized using the equation provided in gn8
 

Reply to Metal CU in garage T.T system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top