hi all,

been looking at an outbuilding supply on a tt arrangement.
i usually gland the swa near the ccu in a metal enclosure but whats peoples thoughts on using a metal enclosure on tt?

cheers
 
531.4.1 is the reg number applicable.

If you think about it, if there is a fault between the phase and the metal enclosure and the metal enclosure is earthed. Because its TT it'll have a Zs of >10ohms. So if it is 10ohms and there is a dead short between phase and enclosure - 23A will flow, not enough to trip a 20A breaker, might work on smaller breakers. If Ze is higher then dead short wouldn't even trip a 6A breaker.
 
Generally the metal enclosure should be RCD protected....if the only RCD is within the metal enclosure it wont be protectd against a fault between the incoming supply and the enclosure .
If you take additional steps to ensure the incomer cant short onto the enclosure this is deemed satisfactory....but IMO it is not and an insulated enclosure should always be used.
 

Reply to metal enclosures on tt in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
715
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top