hi all,
been looking at an outbuilding supply on a tt arrangement.
i usually gland the swa near the ccu in a metal enclosure but whats peoples thoughts on using a metal enclosure on tt?
cheers
531.4.1 is the reg number applicable.
If you think about it, if there is a fault between the phase and the metal enclosure and the metal enclosure is earthed. Because its TT it'll have a Zs of >10ohms. So if it is 10ohms and there is a dead short between phase and enclosure - 23A will flow, not enough to trip a 20A breaker, might work on smaller breakers. If Ze is higher then dead short wouldn't even trip a 6A breaker.
Generally the metal enclosure should be RCD protected....if the only RCD is within the metal enclosure it wont be protectd against a fault between the incoming supply and the enclosure .
If you take additional steps to ensure the incomer cant short onto the enclosure this is deemed satisfactory....but IMO it is not and an insulated enclosure should always be used.
Reply to metal enclosures on tt in the Australia area at ElectriciansForums.net
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...