Hi

Has anybody ever found where this "rule has come from"? In the NAPIT codebreakers book it quotes "ESQCR regs" but it is not actually written in there. If it is a DNO rule then it comes under their regs (ESQCR), but as I said, it is not in there....
 
I think different DNOs sometimes have slightly different requirements, but the 3M rule is a good rule of thumb and should ensure compliance.
 
It’s the DNO’s fuse for protecting their equipment, not for protection of the consumers side, other than what they allow which is typically 3 meters.
Not that they police it mind.
I also wouldn’t code it on an EICR tho for tails longer than this, provided that the fuse offered fault protection.
 
DNO requirements
It's important to remember that their 'requirements' are nothing more than 'nice to haves'. We have no legal or moral duty to comply with them.

I would take a far more case by case approach to the provision of isolation on tails rather than trying to stick religiously to a 3m preference expressed by companies who ultimately have no duristiction over anything past the main head.
 
It's important to remember that their 'requirements' are nothing more than 'nice to haves'. We have no legal or moral duty to comply with them.

I would take a far more case by case approach to the provision of isolation on tails rather than trying to stick religiously to a 3m preference expressed by companies who ultimately have no duristiction over anything past the main head.

I'm not saying you should necessarily stick to it 100%, I was saying it could be a rule of thumb guide to what DNOs sometimes require
 
I believe is DNO rules but not written in stone
This is how it is written in the NAPIT Codebreakers book. If it is "ESQCR" then why is it not listed in there?? How can it be a DNO rule if different DNOs quote different lengths? Here in the westcountry, WPD will not allow sparks to remove the service fuse but in the east of the country the DNO permits it!
 

Attachments

  • Capture.JPG
    Capture.JPG
    21.5 KB · Views: 57

Reply to the thread, titled "Meter tails >3 metres in length" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top