metrel mi3000 testing for ze | Page 2 | on ElectriciansForums
Discuss metrel mi3000 testing for ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
continuity of rfc
R1 = 0.2
R2 = 0.2
RN = 0.3
R1+R2 = 27.9 furthest socket from cu
R1+RN = 0.1 furthest socket from cu
Could you explain how you obtained these reading a bit more please,.....they really don't add up at all????
Alright lads
lenny ive popped back to re do the rfc test and got practically the same readings
R1=0.2
R2=0.2
RN=0,1
then connected incoming line to outgoing earth and outgoing line to incoming earth
R1+R2= 29.9 fail
then changed my earths to the neutrals and got
R1+RN= 0.0
any ideas whats up and do i have to rectify the problem for my cu assessment?
Alright lads
R1=0.2
R2=0.2
RN=0,1
R1+R2= 29.9 fail
R1+RN= 0.0
Are you sure you have the ends of the ring correctly identified?
Alright lads
R1=0.2
R2=0.2
RN=0,1
R1+R2= 29.9 fail
R1+RN= 0.0
It sounds to me that at one of the socket-outlets the CPC and neutral are swopped over.
Cheers fellas
i,ll check the sockets as customer has said about ten years ago the kitchen was wired in by a relative so hopefully the problem lies in there
hi i have the metrel mi3000 easi test and one of the lads i work with did a ze test using my meter set to loop z (rcd) he went between the live neutral of the main switch and earth and said that the meter froze. I have checked all the fuses and nothing has blown but i cant get to loop rcd anymore. any ideas? please help!
I sometimes have problems, doing Zs tests, if the contact with the probes is not very good.
If your meter has frozen, try removing the batteries, leaving a couple of minutes (have a cup of tea or something) and the replace the baterries and re-try.
If that doesn't work, then you will have to return the unit for repair.
Have you tried the universal method of repair......blowing on it???:lol:
I'd agree with spin above though, if pulling the batteries out doesn't cure it you may have to send it away.
thanks iv tryed doing that and still no joy. i just wanted to make sure that before i send it back that its not something that would void the warrenty. also wheres the thanks buttons im new to this!
Along the bottom of each post is a brown "bar". At the left hand end is the "thanks" button.
Hi just a thought but is it set to test TN/TT in settings menu.To access settings menu press backlight key and turn function selector switch,to leave set up rotate selector switch again.
Reply to metrel mi3000 testing for ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
"When stoned..." Brilliant!