Hi kelrich, i have a similar prob with a friends installation, i put the post on yesterday "this is odd". I can get a Zs from a SO, but when i try get a Ze, meter wont test. I have a metrel similar to yours and it has a display giving PD between L & N and L & E prior to test. The readings i get are very odd. Thought it might be leads, but they're ok.
Theres some views on the post that marry up somewhat with lenny's above and others. Av a look.
esc
I have a Metrel MI3100 and a similar thing happened to me today, Ze test with earth conductor disconnected - PD between L-E 210v, PD between N-E 42v, total 252v - Metrel refused to test with error message of unrecognised supply. Reconnected earth conductor and re-tested works fine with sensible reading and PDs 230v and 0v as expected. Did you ever get a conclusive answer as to what was happening in your case?