Lenny, thanks for response but I kinda new sheath is adequate, but was after a csa to put down on a test sheet. I have an existing supply to a garage . . . . . . any way you know the story. It's funny how the csa of swa is readily available but I have scoured the web but canna find anything for MI.Hi Lurch.
The only answer I can give is that the sheath of a pyro cable is ALWAYS sufficient to be used as the CPC and ALWAYS complies with BS 7671.
As for the actual physical size.....maybe a call to the manufacturer???
SWEET!! where did you dig that one ? Top man!!Found this.....
Cross sectional area in mm squared
Effective area of cable sheath
2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2
2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2
2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2
2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2
2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2
2L4 ****** 11 mm2
2H4 ****** 16 mm2
2H6 ****** 18 mm2
3H6 ****** 20 mm2
2H10 ****** 24mm2
3H10 ****** 27mm2
2H16 ****** 30mm2
3H16 ****** 34mm2
Hope this helps you.
What cable type does it look like? T&E?Hiya Guys. While testing in communal blocks I am coming across ST and SH for the cpc size on the circuit charts. Can someone tell me what these represent please
It would be helpful if you told us what the wiring and / or wiring method is. I'm assuming that SH is possibly Sheath and ST is Steel conduitHiya Guys. While testing in communal blocks I am coming across ST and SH for the cpc size on the circuit charts. Can someone tell me what these represent please
Hiya Yea sorry it is run in Pyro on both accounts. I did guess the SH meant sheath but couldnt think of ST meantIt would be helpful if you told us what the wiring and / or wiring method is. I'm assuming that SH is possibly Sheath and ST is Steel conduit