can someone advise where I can establish the CSA of the sheath of MICC please?

Thx in advance..... Lurch
 
Hi Lurch.

The only answer I can give is that the sheath of a pyro cable is ALWAYS sufficient to be used as the CPC and ALWAYS complies with BS 7671.

As for the actual physical size.....maybe a call to the manufacturer???
 
Hi Lurch.

The only answer I can give is that the sheath of a pyro cable is ALWAYS sufficient to be used as the CPC and ALWAYS complies with BS 7671.

As for the actual physical size.....maybe a call to the manufacturer???
Lenny, thanks for response but I kinda new sheath is adequate, but was after a csa to put down on a test sheet. I have an existing supply to a garage . . . . . . any way you know the story. It's funny how the csa of swa is readily available but I have scoured the web but canna find anything for MI.

Any body else out there had this scenario and over come it?
 
Found this.....;)


Cross sectional area in mm squared
Effective area of cable sheath

2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2


Hope this helps you.
 
Found this.....;)


Cross sectional area in mm squared
Effective area of cable sheath

2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2


Hope this helps you.
SWEET!! where did you dig that one ? Top man!!
 
Hiya Guys. While testing in communal blocks I am coming across ST and SH for the cpc size on the circuit charts. Can someone tell me what these represent please
It would be helpful if you told us what the wiring and / or wiring method is. I'm assuming that SH is possibly Sheath and ST is Steel conduit
 

Reply to MICC - sheath csa in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Ignore the post in #3 it is of no help. Hopefully someone may know but it maybe a longshot, have you asked on a more specific appliances forum?
Replies
2
Views
408
It could be a slave switch where you would have a L in and a common wire out to a master switch.
Replies
3
Views
588

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top