Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083
Circuit 1L1
Assuming we can use 1.5mm cpc
R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms
ZS = 0.083 + 0.10 = 0.183
Ia = 230 / 0.183 = 1,256a
S = 1,256 squared x 0.1 = 157753 square root this figure / 115 = 3.45mm cannot be right surely??
Bear in mind that with sufficient current the device may open in the definite minimum time of 0.01 seconds rather than the 0.1s "instantaneous" figure in the Appendix.
So that calculation now becomes Assuming we can use 1.0mm cpc
R1 + R2 = (12.10 + 18.10) x 1.2 x 3.57 / 1000 = 0.129ohms
ZS = 0.083 + 0.129 = 0.21ohms
Ia = 230 / 0.21 = 1,095a
As a 60898- C will trip in 0.4s at 60a this figure will be used
S = 60 x 0.4 / 115 = 0.32mm
Reply to minimum cpc sizes in the UK Electrical Forum area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...