minimum cpc sizes
S
SafetyEICR
Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083
Circuit 1L1
Assuming we can use 1.5mm cpc
R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms
ZS = 0.083 + 0.10 = 0.183
Ia = 230 / 0.183 = 1,256a
S = 1,256 squared x 0.1 = 157753 square root this figure / 115 = 3.45mm cannot be right surely??
S = 1,256 squared x 0.1 = 157 square root this figure / 115 = 3.45mm cannot be right surely??
You have done the maths right but it should show 157,000.
However, a 6A mcb (if that's what you have) will trip in 0.1s at 30A so that is the current that should be used.
30² x 0.1 = 90
√90 / 115 = 0.08mm²
Bear in mind that with sufficient current the device may open in the definite minimum time of 0.01 seconds rather than the 0.1s "instantaneous" figure in the Appendix.
So I need to replace 0.1 with 0.4. as the circuit is 240v <32a. Just a little confused as we were shown a different way by our course tutor. thanks for feedback.
So that calculation now becomes Assuming we can use 1.0mm cpc
R1 + R2 = (12.10 + 18.10) x 1.2 x 3.57 / 1000 = 0.129ohms
ZS = 0.083 + 0.129 = 0.21ohms
Ia = 230 / 0.21 = 1,095a
As a 60898- C will trip in 0.4s at 60a this figure will be used
S = 60 x 0.4 / 115 = 0.32mm
SafetyEICR,
bartkusal,