Darren-Sparky

hi, today i installed a 8 way mk rcd i had from left to right;

100a main switch
63a rcd

40a mcb cooker
32a mcb ring main
16a mcb immersion
6a lighting up
6a lighting down

tns system, i did my tests before i installed new consumer unit and all was good, when i tried to turn on cu the rcd would trip immediately, but other times i could turn on the cu and rcd would stay on but as soon as i plugged anything in to a socket or switched a light on the rcd tripped? also the test button would not operate i replaced the rcd with 3 new ones just incase and all the same results an intermittent fault that never really occurred more than once.

ive checked polarity of incoming tails and all seems good, i also couldnt get rcds to trip using my rcd tester,

any help would be appreciated

thanks
 
hi yes my thoughts exactly but, using a spare mcb i isolated all other circuits and run 1meter of 2.5mm twin and earth to a temporary socket and plugged my battery charger in and as soon as i switched on the rcd trips instantly,
 
no i left neutrals connected, but with all mcbs off the rcd stays on,

i then turn mcbs on one at a time and the rcb stays on

as soon as there is any load on any circuit the rcd trips

ive been racking my brains about this for hours thanks for your replys hopefully we can get to the bottom of this
 
Think about it Darren, why would the RCD hold until there's a load?
It's N-E. It has to be.
I'm really not sure why you did that thing with the 2.5 and socket. What were you hoping to achieve by that?
Get your tester back out and hunt it down because it's there somewhere mate
 
If you are 100% sure your IR results are good and the configuration of the board is correct, isolate 1 circuit at a time and diss the neutrals for the isolated circuit and repeat until you find the offending circuit.
 

Reply to mk rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Have you notified Building Control of these works?
2
Replies
19
Views
950
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top