First of all, sorry I didn’t take more photos.
Been to a customer to price a job and had a look at his CU. Split RCD half and half.

From this picture, it appears the left hand side rcd is off, although all the circuits are powered.

[ElectriciansForums.net] Most obvious fault here


so. First thought, faulty rcd. Says it’s off but contacts must still be closed.

Further investigation. Turned all breakers off, reset rcd and it held. Tripped on test button.
Reset right hand rcd.... also held.
Turned on circuit 1, which is marked as sockets, (first one off right hand, not in picture) trips LEFT hand rcd.

Without detailing any more, it appears the left hand side bank of breakers are being supplied through the right hand side rcd. Possibly because they’ve mixed up the rfc legs. All the load on the left hand side running through one 2.5mm cable. I think I’ll clamp it out of interest.
Would this happen with just lives mixed, just neutrals, or both?

I’ll update early next week. With more photos
 
"do not megger alarms". a niceic approved sticker. can't they get terminology correct? and it's pi$$ed.
Looks more like an AICO sticker (maybe NIC approved) but def an Aico sticker that is included in the detector box.
[automerge]1594972619[/automerge]
Would this happen with just lives mixed, just neutrals, or both?
Please post your findings, I'm sure we would all like to know the outcome!
 
I would check the neutrals first, especially the rcd neutrals are on the correct neutral bars. Came across something similar a couple of years ago. You could also check the legs of any ring mains are not crossed over.
[automerge]1594975810[/automerge]
When it says do not megger alarms, it's not talking about the brand of tester. It's telling you not do a Insulation Resistance Test on the alarm circuit as it is vulnerable to the test voltage.
 
Last edited:
I would check the neutrals first, especially the rcd neutrals are on the correct neutral bars. Came across something similar a couple of years ago. You could also check the legs of any ring mains are not crossed over.
[automerge]1594975810[/automerge]
When it says do not megger alarms, it's not talking about the brand of tester. It's telling you not do a Insulation Resistance Test on the alarm circuit as it is vulnerable to the test voltage.
Welcome to the forum. We know I was being sarcastic, for a manufacturer to state "do not megger" is pretty poor terminology.
 
The implication of the label is that it is not O.k use an insulation tester manufactured by Megger, but by default it would be acceptable to use any other make tester to carry out an Insulation test.

As Westwood, it's wrong for any manufacturer to use that term.
 
Do not “megger” alarms, hear you loud and clear through the “klaxon” and remember to clean up afterwards with the “hoover”

After you've parked up outside on the "tarmac" make sure to take notes with your "biro" about what you find inside. Hopefully it's not a handful of discarded "fibreglass" insulation or "bubble wrap". Take care not to break those flimsy Hager lids or you might have to fix it with "super glue" "sellotape" or "velcro"
 
"do not megger alarms". a niceic approved sticker. can't they get terminology correct? and it's pi$$ed.
Why do you think NICEIC approved this? It's Aicos own sticker?

I've mentioned it to Aico a couple of times that there is no such test as 'meggering'. I dont think they can spell insulation :tearsofjoy:
 
After you've parked up outside on the "tarmac" make sure to take notes with your "biro" about what you find inside. Hopefully it's not a handful of discarded "fibreglass" insulation or "bubble wrap"....

Never knew that "fibreglass" was a brand name - some more new information for today :thumbsup:

It does seem pretty unprofessional for a company like Aico to use a brand name in place of the correct term. Maybe they hope to start a trend and this is a subtle way of encouraging electricians to reference "Aicos" in place of "smoke detectors" ?
 

Reply to Most obvious fault here in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
I misread it.
    • Like
Replies
13
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top