First of all, sorry I didn’t take more photos.
Been to a customer to price a job and had a look at his CU. Split RCD half and half.
From this picture, it appears the left hand side rcd is off, although all the circuits are powered.
so. First thought, faulty rcd. Says it’s off but contacts must still be closed.
Further investigation. Turned all breakers off, reset rcd and it held. Tripped on test button.
Reset right hand rcd.... also held.
Turned on circuit 1, which is marked as sockets, (first one off right hand, not in picture) trips LEFT hand rcd.
Without detailing any more, it appears the left hand side bank of breakers are being supplied through the right hand side rcd. Possibly because they’ve mixed up the rfc legs. All the load on the left hand side running through one 2.5mm cable. I think I’ll clamp it out of interest.
Would this happen with just lives mixed, just neutrals, or both?
I’ll update early next week. With more photos
Been to a customer to price a job and had a look at his CU. Split RCD half and half.
From this picture, it appears the left hand side rcd is off, although all the circuits are powered.
so. First thought, faulty rcd. Says it’s off but contacts must still be closed.
Further investigation. Turned all breakers off, reset rcd and it held. Tripped on test button.
Reset right hand rcd.... also held.
Turned on circuit 1, which is marked as sockets, (first one off right hand, not in picture) trips LEFT hand rcd.
Without detailing any more, it appears the left hand side bank of breakers are being supplied through the right hand side rcd. Possibly because they’ve mixed up the rfc legs. All the load on the left hand side running through one 2.5mm cable. I think I’ll clamp it out of interest.
Would this happen with just lives mixed, just neutrals, or both?
I’ll update early next week. With more photos