Scott - good evening. I'll think on your last post tonight and reply tomorrow - I get up early.
Could you describe/draw how the motor is actually now connected to the B-C starter by reference to the motor terminals (my As1-4 and Zs1-2) and the starter terminals (Us1-4 and Z)? If wiring has been done as I advised then A4 is a permanent N so Z2 can be connected to it - and thus no need for a fifth wire from Z2 back to the starter to connect to N.
I would appreciate it if you could take some voltage measurements at the input to the starter as I mentioned for the stop, start and run phases.
Could you describe/draw how the motor is actually now connected to the B-C starter by reference to the motor terminals (my As1-4 and Zs1-2) and the starter terminals (Us1-4 and Z)? If wiring has been done as I advised then A4 is a permanent N so Z2 can be connected to it - and thus no need for a fifth wire from Z2 back to the starter to connect to N.
I would appreciate it if you could take some voltage measurements at the input to the starter as I mentioned for the stop, start and run phases.
Last edited: