OP
Knobhead
Squirrel cage motors.
Should have done this first really, but I’m not the best organised person.
This shows an exploded view of a motor to give some idea of what goes where.
The motor can be star or delta connected.
If needs be to allow star delta starting. (See other posts)
The basic windings are brought out to the terminal box. Shown here as Delta to the left and Star to the right.
Delta terminal box
Star terminal box
The rotating field is created by the 6 coils for a 2 pole motor by the rotation phase rotation of the three phase supply
The motor gets it’s name from the construction of the rotor windings. Take away the rotor laminations you have a squirrel cage.
Transformer induction induces a fixed field on the rotor cage. The cage rotates in an attempt to catch up with the rotating stator field. A forlorn hope as there has to be a certain amount of slip to give the induced current to give rotation and torque.
Early motors had copper bars brazed to copper end rings. Later the copper was replaced by aluminium injection to form a solid casting.
The cage could be in several forms.
A standard cage that would give normal acceleration and torque
Double cage where due to the higher flux density on the inner bars at high slip would give twice the torque on start up. It had the down side of higher inrush current.
Modern cages are a highbred of both. With aluminium injection these are easier to make now.
There are a few companies now doing copper injection for the cage.
As for the motor being constant speed, I’m afraid that’s a myth. As load increases more slip is needed to produce the torque. The motor name plate gives speed at a % of loading.
Delta terminal box
Star terminal box