Squirrel cage motors.

Should have done this first really, but I’m not the best organised person.

This shows an exploded view of a motor to give some idea of what goes where.

View attachment 12926

The motor can be star or delta connected.
If needs be to allow star delta starting. (See other posts)

View attachment 12927

The basic windings are brought out to the terminal box. Shown here as Delta to the left and Star to the right.

View attachment 12928
Delta terminal box

View attachment 12929
Star terminal box


The rotating field is created by the 6 coils for a 2 pole motor by the rotation phase rotation of the three phase supply

View attachment 12930

View attachment 12931

The motor gets it’s name from the construction of the rotor windings. Take away the rotor laminations you have a squirrel cage.

Transformer induction induces a fixed field on the rotor cage. The cage rotates in an attempt to catch up with the rotating stator field. A forlorn hope as there has to be a certain amount of slip to give the induced current to give rotation and torque.

Early motors had copper bars brazed to copper end rings. Later the copper was replaced by aluminium injection to form a solid casting.
The cage could be in several forms.

A standard cage that would give normal acceleration and torque
View attachment 12932

Double cage where due to the higher flux density on the inner bars at high slip would give twice the torque on start up. It had the down side of higher inrush current.
View attachment 12933

Modern cages are a highbred of both. With aluminium injection these are easier to make now.
View attachment 12934

There are a few companies now doing copper injection for the cage.

As for the motor being constant speed, I’m afraid that’s a myth. As load increases more slip is needed to produce the torque. The motor name plate gives speed at a % of loading.
 
i always get confused with motors star and delta and how , have no problem fixing faults with them then again i am a tad odd , nice post tony
 
Very helpful Tony, cheers mate.
 
Was braught up in another thread but here's some bumf on artificial 3phase motor connections.

Now this is taken from my little motor bible and is the only way I've seen in person a 3ph motor run on single phase.

[ElectriciansForums.net] Motors


[ElectriciansForums.net] Motors


This is another way of connecting it up, now I've only ever read the theory about this. Never seen it in the real world. It's called a steinmetz connection.

[ElectriciansForums.net] Motors


I'll write a post with the theory explained when I can spend some time and edit it properly, rather than on my phone.
 
Primary resistance starter

Primary resistance starter

I’ve only ever seen two of these, they were used on lift motors.

As you can see from the drawing they are pretty simple. On start up contactor K2 closes allowing a reduced voltage to the stator windings, after a short time delay contactor K1 closes and K2 drops out.
They suffer from being limited to X number of starts per hour due to heat build up.

View attachment 14202

View attachment 14201
 
Re: Primary resistance starter

Primary resistance starter

I’ve only ever seen two of these, they were used on lift motors.

As you can see from the drawing they are pretty simple. On start up contactor K2 closes allowing a reduced voltage to the stator windings, after a short time delay contactor K1 closes and K2 drops out.
They suffer from being limited to X number of starts per hour due to heat build up.

View attachment 14202

View attachment 14201

Is this not just effectively a liquid starter?

Any advantage to this design?
 
Liquid starters are normally used on slip ring motors where isolation of the phases isn’t as important. There’s no reason a liquid starter couldn’t be used as a primary resistance but it would need major re-engineering to make it safe. Instead of one earthed tank for the electrolyte, three separate insulated tanks would be needed. There was a company in the 70/80’s that made Statormatic starters, the same company made Vapormatic starters for slip-ring motors.
View attachment 14208
Slip ring rotor
View attachment 14207
Stator
 
Delt with a lot of liquid starters at the cement plant I used to work, usually with 3.3kv drives, had a few long days when the brush gear flashed over with carbon dust, we did try to blow them oh weekly but production often superseded maintenance.

I was just thinking about the therory behind it, am I right in thinking a star delta starter would be a cheeper way of setting this up? I take it the resistor bank is used for the same reason the liquid starters are used? Never seen that set up before.
 
The primary resistance has the beauty that it’s flexible as to the % of torque at start up. Star/delta is 1/√3 only.

The beauty of a slip ring motor is it’s high starting torque, something you wouldn’t get with start/delta. A cement mill would just sit there and not move in star. On top of that even at √3 of the DOL starting current (say 6X FLC/√3 = 3.46X FLC) the 3.3 OCB would trip on instantaneous overload. The cement mills I’ve worked on ranged from 900 to 6000HP, I wouldn’t like to be around when the breaker opened. I was stood in front of a 3.3 ACB when that tripped due to a slip-ring flashover, I near had to go and change my underpants.
For heavy starting loads you can’t beat slip-ring motors.

Some I’ve worked on were variable speed using the Kramer system. They started using a liquid starter. Once at full speed the Kramer control would kick in and regulate the current in the rotor, the recovered energy being fed back in to the 11KV system via an inverter and step up transformer.
View attachment 14214
 
We had a system very similar to that tuning one of the kiln firing fans, it was an abb multidrive invertor 2Mva, that used a resistor bank to start and also managed to recover energy from the drive.

Never got my head around how that worked, it was only on site a couple of months before I left. Was delivered in a steel container as a plug and play system, it weighed 27tonnes.
 

Reply to Motors in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
178
That sounds to be more of a control issue rather that a motor issue Are all the limit switches working properly and not sticking occassionally
Replies
1
Views
397

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top