Just after people opinions on this.
I ve just finished installing a kiosk which supplies 3 buildings,
The DNO was not clear on the earthing system they would be providing, in case I ended up with PME I earthed the submain armouring only at the kiosk
(2 core SWA) and isolated it at the load end with a stuffing gland into metal clad board. Earthing was provided for locally at each outbuilding with a rod - readings all good.
When the DNO turned up they fitted a cut out with earth bar on the side PME style but said I couldn’t use it because of high network ELI. No problem I fitted a 100mA types S after meter to provide earth fault protection on my submains.
Everything’s up and running but now wish I’d use standard SWA glands to tie all the earthing together and put all the rods in parallel.
I am pretty sure it’s compliant as is but am tempted to fit the glands all tho it won’t be fun.
Whats the general concensus?
Cheers
I ve just finished installing a kiosk which supplies 3 buildings,
The DNO was not clear on the earthing system they would be providing, in case I ended up with PME I earthed the submain armouring only at the kiosk
(2 core SWA) and isolated it at the load end with a stuffing gland into metal clad board. Earthing was provided for locally at each outbuilding with a rod - readings all good.
When the DNO turned up they fitted a cut out with earth bar on the side PME style but said I couldn’t use it because of high network ELI. No problem I fitted a 100mA types S after meter to provide earth fault protection on my submains.
Everything’s up and running but now wish I’d use standard SWA glands to tie all the earthing together and put all the rods in parallel.
I am pretty sure it’s compliant as is but am tempted to fit the glands all tho it won’t be fun.
Whats the general concensus?
Cheers