Discuss My 1st board on site advice in the UK Electrical Forum area at ElectriciansForums.net
I'm certain that there is, or at least used to be. Won't have access to my BS7671 until the weekend though.514.4.3 PEN conductor A PEN conductor shall, when insulated, be marked by one of the following methods:
(i) Green-and-yellow throughout its length with, in addition, blue markings at the terminations
(ii) Blue throughout its length, with green-and-yellow markings at the terminations.
There is no percentage requirement.
For me, if I were inspecting an existing installation.
It would be:
1) no comment, correctly identified PEN conductor,
2) code C3, incorrectly identified protective conductor, or
3) code C2, PEN conductor used in a consumer’s installation fed from a public supply.
If it were an Initial Verification, it would be: Fix that.
For me, if I were inspecting an existing installation.
It would be:
1) no comment, correctly identified PEN conductor,
2) code C3, incorrectly identified protective conductor, or
3) code C2, PEN conductor used in a consumer’s installation fed from a public supply.
If it were an Initial Verification, it would be: Fix that.
I'm certain that there is, or at least used to be. Won't have access to my BS7671 until the weekend though.514.4.3 PEN conductor A PEN conductor shall, when insulated, be marked by one of the following methods:
(i) Green-and-yellow throughout its length with, in addition, blue markings at the terminations
(ii) Blue throughout its length, with green-and-yellow markings at the terminations.
There is no percentage requirement.
Yes and the colour denotes the size of the ferrule. You can't match the colour of the ferrule to the function of the conductor.
Anyone looking at it will be able to see that the colour ring is the ferrule and has not been fitted to indentify the function of the conductor.
View attachment 48660
The 3 loose ferrules on the right, are all blue.
Here’s the thing:
I am neither French or German, and I’m not working in either of those countries.
I’m English and I work in the UK, to UK Regulations.
I have been known to work abroad and to the Regulations that pertain to that country.
Then again I’ve worked abroad and used UK Regulations.
Only places I know of in the UK, which use non-UK Regulations are American Air Bases and quarters.
At the end of the day, you have a choice.
Comply with the Regs, or don’t comply with them.
You can easily remove the coloured ‘insulation’ from the ferrule, either before or after crimping.
So if you don’t remove it, you’ve chosen not to comply.
Yes I would.If you cut the plastic bit off then you are modifying a product and using it in a manner other than in accordance with manufacturers instructions. So if you remove it you don't comply with regulations, to the same degree of ridiculous pettiness as thinking a ferrule is a cable marker in the first place.
Perhaps you could answer the question about whether you would code the use of standard red, blue and yellow crimps as a non-compliance?
Here’s the thing:
I am neither French or German, and I’m not working in either of those countries.
I’m English and I work in the UK, to UK Regulations.
I have been known to work abroad and to the Regulations that pertain to that country.
Then again I’ve worked abroad and used UK Regulations.
Only places I know of in the UK, which use non-UK Regulations are American Air Bases and quarters.
At the end of the day, you have a choice.
Comply with the Regs, or don’t comply with them.
You can easily remove the coloured ‘insulation’ from the ferrule, either before or after crimping.
So if you don’t remove it, you’ve chosen not to comply.
Whilst your Emailing them about that, could you ask them whether BS 7288 sockets and FCUs being used for additional protection?Being the french or german colour scheme is just something that has become standard world wide as they were the ones who began mass producing them.
Absolutely nothing to do with working to their regulations.
By removing it, you've breaking other regs of not following manufacturers instructions.
On a side note, you can buy them without the plastic collar for anyone wondering.
I'll email a couple of the guys that I know in the IET/BSI Technical Committee, I'll come back with a response. They could use a laugh.
If I'm wrong I'll hold my hands up to it.