Hello,

I have just competed my 1st consumer unit install on site. I would like some advice on how I may improve the quality/neatness.

All constructive criticism welcome

Thanks

[ElectriciansForums.net] My 1st board on site advice


[ElectriciansForums.net] My 1st board on site advice
 
S

So if I have not cut the fly leads it’s not a requirement for ferrules ?
Before cutting any neutral or functional earth leads, first check Manufacturer’s Information to ensure they can be cut.
Fine and very fine wires do need protection when used with screw terminals.
For years the practice has been to twist and double over the ends, most commonly in plug tops and lamp holders.
The manufacturers tend to weld the strands together, or crimp them with a ferrule.
Leaving the leads long makes for a messy board, and leaving the leads coiled up creates it’s own problems.
Using ferrules is neat, allows for easier termination and looks quite professional. Just remember not to use Blue insulated ferrules on earth wires.
 
Strictly speaking that's true. But I think anyone opening a DB will be able to identify the difference between a blue ferrule and a marker.applied to. Identify a PEN conductor.
Ferrules come in a variety of colours, blue, red, black, white, yellow, orange, grey, green.
That’s just the colours I’ve got.
Not using a blue on earth conductors, or stripping off the blue insulation, is not difficult.
I guess it all depends on whether you want to adhere to the Regulations or not?
 
Ferrules come in a variety of colours, blue, red, black, white, yellow, orange, grey, green.
That’s just the colours I’ve got.
Not using a blue on earth conductors, or stripping off the blue insulation, is not difficult.
I guess it all depends on whether you want to adhere to the Regulations or not?

Ferrules are not cable identifiers.

An yes they do come in lots of colours determined to size. 99% of ferrules will follow either the french or german coloring system. (In the UK it's mostly french)
 
In the UK, blue at the termination of a G/Y wire denotes a PEN conductor.

A few mm of blue ferrule on the end of a length of G/Y won't confuse anyone. And if you're going to be that picky then the ferrule insulation should be green/yellow stripe :)
 
It wouldn't meet the percentage requirements for identification anyway (15% off the top of my head).
514.4.3 PEN conductor A PEN conductor shall, when insulated, be marked by one of the following methods:
(i) Green-and-yellow throughout its length with, in addition, blue markings at the terminations
(ii) Blue throughout its length, with green-and-yellow markings at the terminations.

There is no percentage requirement.
 
For me, if I were inspecting an existing installation.
It would be:
1) no comment, correctly identified PEN conductor,
2) code C3, incorrectly identified protective conductor, or
3) code C2, PEN conductor used in a consumer’s installation fed from a public supply.

If it were an Initial Verification, it would be: Fix that.
 
I have never, an I'm not going to start now. Classed a ferrule as a cable marking.

Opening that up leads to all sorts of pedantic situations.
Complying with the Regulations is obviously a matter of choice.
If you sign the declaration on an EIC or MEIWC that you have designed, constructed and inspected in accordance with BS7671, you could be found guilty of an offence of fraud.
 
Ferrules come in a variety of colours, blue, red, black, white, yellow, orange, grey, green.
That’s just the colours I’ve got.
Not using a blue on earth conductors, or stripping off the blue insulation, is not difficult.
I guess it all depends on whether you want to adhere to the Regulations or not?

Yes and the colour denotes the size of the ferrule. You can't match the colour of the ferrule to the function of the conductor.

Anyone looking at it will be able to see that the colour ring is the ferrule and has not been fitted to indentify the function of the conductor.
 

Reply to My 1st board on site advice in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K
  • Question
I’d say yes go for it.
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top