Thanks of the advice guys appreciate it. I strive improve my quality in my work.
C
Could your link me to the BS7671 requirement please ?
The earthing tail from the MET, is that provided by the manufacturer?
Off the top of my head regulation 526.2 or there about.
Look for fine stranded conductors.
Off the top of my head regulation 526.2 or there about.
Look for fine stranded conductors.
A) Proteus is cheap S***
B) You need ferrules on the end of those neutral fly leads.
C) I don't like to see cable ties holding conductors together in a CU
Although at a quick glance aside from the above. Looks ok
Also could you expand a little on B about the cable ties. I used that for aesthetically purposes.
526.9 Connection of multiwire, fine wire and very fine wire conductors
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
526.9.2 Soldering (tinning) of the whole conductor end of multiwire, fine wire and very fine wire conductors is not permitted if screw terminals are used.
526.9.3 Soldered (tinned) conductor ends on fine wire and very fine wire conductors are not permissible at connection and junction points which are subject in service to a relative movement between the soldered and the non-soldered part of the conductor.