Put this in today, I hope it doesn't burst into flames.:tongue3: Didn't have the time to faff about and get the cabling 'perfect' as I had so much to do today but I think it's ok. With the BG boards I generally 're number' the earth bar as to me it's illogical having the CPCs running in the opposite order of the neutrals,I'll miss the insulated CUs. Sorry about the
poor photo. :)
WP_20151221_16_12_30_Pro.jpg
 
Not being critical, but seeing as this is a hi integrity unit, why don't you leave a blank between the main switch and RCD1? It looks like you have space
 
I wonder what your client will think in a weeks time if they find out their newly installed board no longer complies with current regulations?
I've been installing Am3 boards since the BYB. I think it's poor practice not to give clients up to date installations whether you agree with new regulations or not.
 
I wonder what your client will think in a weeks time if they find out their newly installed board no longer complies with current regulations?
I've been installing Am3 boards since the BYB. I think it's poor practice not to give clients up to date installations whether you agree with new regulations or not.

How do you know the OP didn't offer both options?
 
"Did not have the time to faff about, too much on, think it will be ok" you are falling into the "that will do" category, not a good sign, every customer deserves the best, your reputation is worth more than anything, always give 100% it will pay off in the long term.
 
"Did not have the time to faff about, too much on, think it will be ok" you are falling into the "that will do" category, not a good sign, every customer deserves the best, your reputation is worth more than anything, always give 100% it will pay off in the long term.
Those of us that operate in the real world don't have time to make it look like a masterpiece, Dave's example is perfectly neat and acceptable IMO.
 
Yes Nice Job , Is that not a gray cable in circuit 4 ? , I have noticed that since we started using brown cables they don't seam to ever use the same shade, I know reds were slightly different but not as much as the browns
 
And AMD2 fuseboards will still be installed by muppets and builders until they run out in 2016

Very true Murdoch. But they will never run out, because as we all know they only catch fire in houses! Never in shops etc!!! They will probably just get more expensive due to less demand. :tounge_smile:
 
Put this in today, I hope it doesn't burst into flames.:tongue3: Didn't have the time to faff about and get the cabling 'perfect' as I had so much to do today but I think it's ok. With the BG boards I generally 're number' the earth bar as to me it's illogical having the CPCs running in the opposite order of the neutrals,I'll miss the insulated CUs. Sorry about the
poor photo. :)
View attachment 31007

How are the BG boards now mate? I sort of stopped using them around a year ago due to poor screws/terminal blocks, and having to bin numerous MCBs due to the bottom cage clamp grounding out. If that's the correct terminology!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Dave OCD

Mentor
Esteemed
Arms
-
Joined
Location
Cornwall
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Hendry Electrical Services

Thread Information

Title
My last 'non Amd 3' CU Install.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
254
Unsolved
--

Advert

Thread statistics

Created
Dave OCD,
Last reply from
Dan,
Replies
254
Views
20,894

Advert

Back
Top