Agreed apart from the few minutes remark.
That said I would rather test every socket upon energising
Energising and then live testing would be O.k if there is no-one else likely to be put at risk of using an incorrectly wired socket or appliance and there is no risk of fire etc.
Just to make clear, incase anyone reading this didn't know, a Martindale socket tester will not pick up a neutral/earth crossed connection which is why the correct dead tests are so important.
I always carry out the sequence of tests in the order I was taught at college, I do a Ze test before starting the design for a new installation, all the rest of my live testing is done after all the dead testing has been done. I only do new installations though so that is why I don't rely on Zs testing, I just use calculation.
You don't record r1 + rn, but you do do it. Look in on site guide, how to test a ring. Tells you step by step.
If you have got red on site guide, bottom of page 81. Continuity of ring final circuits, step 2.
There is also, on pg 38 of GN3, an explanation of (r1+rn)/4