Absolutely. All that said, a thorough R1R2 will pick up cpc in the wrong terminal anyway.

Exactly! Isn't this the point? Even if an R1+Rn wasn't done (which it should be, according to the guidelines) a R1+R2 would still pick up this fault.
And two modular sockets are two separate sockets so both need to be tested. An easy to mistake to make but an error in the testing all the same.......
 
Exactly! Isn't this the point? Even if an R1+Rn wasn't done (which it should be, according to the guidelines) a R1+R2 would still pick up this fault.
And two modular sockets are two separate sockets so both need to be tested. An easy to mistake to make but an error in the testing all the same.......

Yep. Let alone the fact that it was connected wrongly (bad enough on its own), the guy who tested the installation didn't do it properly. Simple.
 
Well as I've never done the 2391, I can only go by my own training and experience.
The r1+rn/R1+Rn tests are listed in GN3 as being step 2 in the testing of an RFC.
However this is often not conducted (especially with new builds) in it's entirety with only the r1+rn part being measured to prove continuity.
With any initial verification, 100% of the installation should be tested, and to my mind this is imperetive when the testing is of a third parties' construction especially as it is likey in this case that there are a number of third parties conducting the construction.
It's all very well taking short cuts when testing your own work, but not when testing other's workand especially when there are likely to be many 'other's'.
With normal double sockets, it is usual to only measure R1+R2 at one of the sockets, so it could be the case that the person conducting the dead tests was not aware that these particular sockets were wired individually, or may be that they knew, but did not consider it necessary to test each individual socket.
This suggests that either the person was inexperienced. Perhaps newly qualified or even not qualified at all.
It may be that the testing is being conducted on a fixed price and the managers/supervisors were pushing for the testing to be conducted quickly, perhaps the person was even instructed not to test each socket?

To my mind, each of the tests listed in GN3 should have been performed in order, and the test and inspection should cover 100% of the installation.
However if the tester has been given an instruction not to conduct certain tests, or not to test 100% of the installation, what can they do?
At the end of the day, they are an employee, and must as such consider that they will be sacked if they don't follow their employers' instructions.
 
Nice one Spin

So are we agreed, that an R1R2, would have picked up the fault, and despite what some books say, R1Rn was not needed? (going away a little from the OP).
 
r1+r2 would have picked it up in this case, but without the r1+rn you could miss a line-cpc reversal. Which of course would be detected at the loop test stage, but that's not really the way. Especially with fancy metal sockets... so r1+rn is essential in my opinion.
 
Visual inspection before testing would help as per inspection schedule. Makes yo wonder how many other suspect installs are out there.

- - - Updated - - -

Visual inspection before testing would help as per inspection schedule. Makes yo wonder how many other suspect installs are out there.
 

Reply to Neutral earth fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
463
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Very technical :D
    • Like
Replies
9
Views
455
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top