What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net
because the neutral from the circuit being fed from the RCBO has to go through the RCBO before it gets to the neutral bar vie the RCBOs neutral lead.....so any imballances due to fault between neutral-earth are seperated from the other RCBOs/RCDs within the install....unless in series of course
Q1 to complete the circuit
Q2 because only one rcbo will detect the imbalance and trip.
because their pigs TC...And why do they have curly neutrals so you can't do a neat job!
Whether post in humour or not the reason is its fine wire and to terminate it it has to be crimped, the factory crimp it for you but if it was just one long lead ppl would shorten it more readily and probably ignore the regs and not crimp, this has a risk of poor termination which can cause overheating, nuisance tripping etc etc, the manufacturers would get more returns thinking rcbo faulty because of poor terminated neutrals due to sparkies cutting long leads to length.And why do they have curly neutrals so you can't do a neat job!
RCBOs have flying neutrals that terminate into a common neutral bar...yes?....so as the final circuit is connected THROUGH each individual RCBO....both line AND neutral.....so the RCBO will detect imballance without upsetting the ballance of any other RCBOs within that C/U....
A - if there was a borrowed neutral then this would trip the rcbo anyway as there is an imbalance of load out and return as the current would be higher on the return path when borrowed neutral load was switched on, but hypothetically if you could maintain the circuit and and then touch down neutral to earth it will only trip the rcbo that is leaking the current and has seen an imbalance, this will depend on many things like where the short is, cable resistance , volts drop etc etc all playing a part in where the neutral current will leak to and how much, its possibly alot more complicated than it should seem.Yea i understand what you mean, what I'm meaning is if there was a borrowed neutral on the load side of the rcbo " a link between two rcbo e.g on two lighting circuits" and there was a earth to neutral fault on one rcbo why won't that affect the rcbo number two ??