What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net
Just to re-iterate kev, when one trips it effectively isolates the other rcbo from the fault so usually on one trips, but occasionally it can trip both together but its rare as background leakage on the circuits will put one rcbo closer to the threshhold than the other as well as trip times and mA needed to trip will very slighty from rcbo to rcbo.
So in a nutshell, several factors are in play as to which one is gonna trip thus its rare for them to trip together, and after one has tripped it blocks the return path so the other rcbo holds.
Correct!Thanks very much Darkwood,
So the reason the path is blocked is because the Neutral has been shut off with RCBO tripping yea, and isnt able to travel back along the neutral lead to the other rcbo? Is that correct?
Correct!
In that instance both will trip.
Hope you can see the fault direction arrows on the last drawing
Correct.As far as I understand it, if there is an N/E fault on RCBO1 and RCBO2 shares a neutral on the load side then RCBO2 will also see an Earth fault and so it will trip.