What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
 
Just to re-iterate kev, when one trips it effectively isolates the other rcbo from the fault so usually on one trips, but occasionally it can trip both together but its rare as background leakage on the circuits will put one rcbo closer to the threshhold than the other as well as trip times and mA needed to trip will very slighty from rcbo to rcbo.
So in a nutshell, several factors are in play as to which one is gonna trip thus its rare for them to trip together, and after one has tripped it blocks the return path so the other rcbo holds.
 
Just to re-iterate kev, when one trips it effectively isolates the other rcbo from the fault so usually on one trips, but occasionally it can trip both together but its rare as background leakage on the circuits will put one rcbo closer to the threshhold than the other as well as trip times and mA needed to trip will very slighty from rcbo to rcbo.
So in a nutshell, several factors are in play as to which one is gonna trip thus its rare for them to trip together, and after one has tripped it blocks the return path so the other rcbo holds.


Thanks very much Darkwood,

So the reason the path is blocked is because the Neutral has been shut off with RCBO tripping yea, and isnt able to travel back along the neutral lead to the other rcbo? Is that correct?
 

Thanks, i was just having a looking at that drawing there on page two tony drew, say for instance there was a neutral to earth fault on RCBO 1 , and it trips RCBO 1, then on RCBO 2,Current flows up the live and back down the neutral as normal, but wont any current flow across that neutral link and touch the earth fault? or how will that work???
 
Last edited by a moderator:
As far as I understand it, if there is an N/E fault on RCBO1 and RCBO2 shares a neutral on the load side then RCBO2 will also see an Earth fault and so it will trip.
Correct.

A borrowed neutral N-E fault will trip both because both neutrals (or shared one) will be connected to earth.


Just to point out that single-module RCBOs are only single-pole switches.
 

Reply to Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
well then, must be a fault on the circuit, a faulty appliance if a power circuit or a faulty RCBO.
Replies
10
Views
1K
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top