Kev2632
What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net
Yes, as no other circuits are connected to it (unless by these faults) none of the other RCBOs will be affected.
Yes.
The term 'Borrowed Neutral' is a bit misleading. Think of it like this -
The first RCBO has a borrowed Neutral from the second RCBO, and...
...the second RCBO has a borrowed Live from the first RCBO so both will have an imbalance.
As I said, if you draw it, it becomes a lot easier to see.
ive PM you and should have explained i was refering to DP rcbo's only you will appreciate throwing a single pole in the mix would have made your confusion worse, but should have gone that route first, it just habit on my part as its what i fit in my control panels but yes domestic is usually single pole.
ive PM you and should have explained i was refering to DP rcbo's only you will appreciate throwing a single pole in the mix would have made your confusion worse, but should have gone that route first, it just habit on my part as its what i fit in my control panels but yes domestic is usually single pole.
Just now, remember and will add to this thread too for other to remember; in a tns and tncs the neutral and earth bar will be linked together if the main switch is on due to the center tap in transformer (tns) and the combined N/E in the cutout on tncs.I replied to your last PM darkwood, I dont have anything back in return? you sure you sent it ? :/
Just now, remember and will add to this thread too for other to remember; in a tns and tncs the neutral and earth bar will be linked together if the main switch is on due to the center tap in transformer (tns) and the combined N/E in the cutout on tncs.
So it shows that an E/N fault feeding back to the E and N bar through 1 or more rcbo's will not effect other rcbo's that are clear of this fault as its not on their load side.
because the neutral from the circuit being fed from the RCBO has to go through the RCBO before it gets to the neutral bar vie the RCBOs neutral lead.....so any imballances due to fault between neutral-earth are seperated from the other RCBOs/RCDs within the install....unless in series of course
This is the way I see it after having a readIs this the case with SP RCBO's as although they supervise the load side N and L they only operate the L phase. In the ideal sittuation each circuit would have its own dedicated earth however if the neutrals are linked at the supply side then where is the break in the circuit in the case of an N-E fault. I would have though an imbalance in current flowing in the faulty neutral wire would also be detected on other RCD's or RCBO's. Clarification on this would be appreciated. The regs seem to explain that a main switch isolator can be used with a seperate RCBO for each circuit but I am unsure if they mean SP or DP RCBO's. DP being mega expensive so quite reluctant to buy these even though I only have 4 ways going out on my current fuse box. Any clarification on this would be much appreciated. Hello to everyone on the forum btw.
Regards
Steve
This is the way I see it after having a read
I think the rcbo, whether single pole -n or double pole,both will disconnect both poles
However, in the single pole rcbos,the live is the rated contacts
The neutrals are not for breaking the load,they operate after the live so do not switch the loads
Hence the neutral tail used, so that it isn't confused with the live terminal
The double pole rcbo has both poles monitored and rated, so no need for the neutral tail, both poles disconnect
In the case of a neutral/earth fault current could flow from the neutral bar through the RCBO to earth through the fault - in which case the RCBO will trip. None of the other RCBOs should trip because there isn't a path to earth through the neutrals of the other circuits. Remember the neutral busbar is 'down wind' of the other RCBOs.Is this the case with SP RCBO's as although they supervise the load side N and L they only operate the L phase. In the ideal sittuation each circuit would have its own dedicated earth however if the neutrals are linked at the supply side then where is the break in the circuit in the case of an N-E fault. I would have though an imbalance in current flowing in the faulty neutral wire would also be detected on other RCD's or RCBO's. Clarification on this would be appreciated. The regs seem to explain that a main switch isolator can be used with a seperate RCBO for each circuit but I am unsure if they mean SP or DP RCBO's. DP being mega expensive so quite reluctant to buy these even though I only have 4 ways going out on my current fuse box. Any clarification on this would be much appreciated. Hello to everyone on the forum btw.