K
Kev2632
What exactly are the neutral leads for? and if a neutral to earth happened on a board with just RCBO'S in it, why doesnt the fault travel along that neutral and affect the other RCBO's?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net
Also in answer to your question is that when the rcbo trips it will stop the current flowing in the borrowed neutral so the second rcbo dosen't see it, which rcbo trips will be down to the variables mentioned above.A - if there was a borrowed neutral then this would trip the rcbo anyway as there is an imbalance of load out and return as the current would be higher on the return path when borrowed neutral load was switched on, but hypothetically if you could maintain the circuit and and then touch down neutral to earth it will only trip the rcbo that is leaking the current and has seen an imbalance, this will depend on many things like where the short is, cable resistance , volts drop etc etc all playing a part in where the neutral current will leak to and how much, its possibly alot more complicated than it should seem.
So it is possible for two rcbos to trip if somebody borrowed a neutral from two different circuits and there was neutral to earth fault on one circuit yea?
And why do they have curly neutrals so you can't do a neat job!
In this set up one rcbo will trip a majority of the time, once it trips it isolates the link to the other rcbo through its double pole switch, although its possible that once in a blue moon they could trip together as you have to remember that if once rcbo gains extra neutral current then the other rcbo will loose it and both are out of balance, but also to take into account is natural leakage existing so the rcbo that has a higher background leakage will operate the first and as mentioned before it then isolates the link between the 2 neutral leaving the other rcbo on.I'm talking about 2 individual rcbo detecting there own circuits what happen if the neutral from rcbo 1 happened to join up with rcbo 2? As in they have borrowed a neutral from circuit 1 and it used at somepoint in circuit 2 would that trip both rcd as the neutrals are mixed up or does it not matter as its one common neutral bar for the installation??? Sorry im just getting confused and cant get my head round this
By Jove i think you got it! correct.... !!!!!!Yea thats probably what it is, neutrals of the same circuit yea? But for example If the neutrals of different circuits were all joined together in 1connector block that will not work ? Because they are fed from two different rcbos is that correct yea? And the rcbo will see an imbalance is that right? Thanks so much for your help so far
Reply to Neutral lead on RCBO'S in the UK Electrical Forum area at ElectriciansForums.net