neutral to earth high voltage | on ElectriciansForums
Discuss neutral to earth high voltage in the UK Electrical Forum area at ElectriciansForums.net
Notts / yorkshire
Been to look at a faulty socket on a rcbo and wont hold in, tried to test trip times etc but reading voltage on earth. Supply is tt, 3ph and 1 ph to a domestic property. Shared earth rod. Cant turn house off as belongs to separate person. So tested voltage at 3 ph db, 230, 400 v etc but got 48v n to e.. so i did insulation test on incoming swa, phase to earth, one down to 350 ohms, n to phase, one 459 ohms, n to e grater than 500 ohms. But can work out why 48v n to earth. House looks to have split load rcds, looking through window. My only conclusions is swa supplying house has low insulation. Am i looking in wrong direction. Ive turned power off to barn till i can look at house supply.
Hi simon, You need to explain the layout better,as order of installations is important,you must have isolated the 3ph to IR test those conductors,so did you turn off the house supply? ....Also,your IR readings need amending :yes:
Are you sure those readings are not Mohms?
High dude,as i now understand it,you NEED to be able to start from incomer,for your testing to be conclusive,which means permission to isolate all that is fed from there,house included.
Although peeping through a window is fun,it does not constitute a comprehensive inspection of that properties installation :yes:
Is it now! :)
True but at first glance on a 3p and 1p tee off on a tt i wouldnt be supprised to see a voltage. Yes it is high but probably nothing to do with the rcbo tripping unless the voltage drops when it is isolated. I suppose people are right its hard ro guess without more info but personally id start with the device upstream as appose to the stray voltage between n and e. If the mft wont test because of pd you could isolate all board app from rcbo with a temp n to e link in to peform them but fck sake dont forget to take it out lol.
Been back and pulled main fuse to house, n to e voltage drops to 3.8v, still couldn't get live test ze, but got L to n ze 0.4 ohms. Rcbo no tests fine with house disconnected. Owner wont let me do insulation test on there swa house supply. So had to leave fault i presum coming from there cable, as boards a dual rcd set up.
If I'm reading this right, you have disconnected one if the other phases going to another board and now the one you are one which is on a different phase now tests correctly?
would I be right in thinking there's a loose neutral on the house supply which is shoving voltage back down the earth?
to be honest I'm just guessing with a stab in the dark, I would need to be there and have it all fully isolated and test it all to know what the issue is.