Been to look at a faulty socket on a rcbo and wont hold in, tried to test trip times etc but reading voltage on earth. Supply is tt, 3ph and 1 ph to a domestic property. Shared earth rod. Cant turn house off as belongs to separate person. So tested voltage at 3 ph db, 230, 400 v etc but got 48v n to e.. so i did insulation test on incoming swa, phase to earth, one down to 350 ohms, n to phase, one 459 ohms, n to e grater than 500 ohms. But can work out why 48v n to earth. House looks to have split load rcds, looking through window. My only conclusions is swa supplying house has low insulation. Am i looking in wrong direction. Ive turned power off to barn till i can look at house supply.