Appreciate your thoughts on this please. New build house, 1 x double garage with studio flat above. The studio flat above will be self contained with small cooker, Imm/Htr etc.
1 Phase PME supply at house. All circuits RCBO's except U/G SWA cable to garage / studio flat. SWA protected by MCB only.
Normally I would fit consumer unit in garage as per norm. But this situation, I'm thinking taking the SWA cable to consumer unit within the studio flat (on top of the garage) then from there using SWA cable to the garage protected by a MCB only.
All circuits within the flat will have to be RCD protected, but I don't want the SWA from there to the garage RCD protected. All circuits within the garage will be RCD protected. The idea being flat and garage electrically 100% separate. Person in flat will have no access to garage.
Hope it al makes sense. Thanks
 
Sorry mate but I think you need a bit more thought on this. How do you propose the studio/flat to be completely electrically seperate if the cut out (such as it is) is in an adjacent house and would require access to it in case of fault? How is metering proposed to be done?
I've not even thought of the garage supply yet, is that supposed to be on with the house? Or is that another independent supply?
Honestly, back to the drawing board for you
:)
 
Sorry mate but I think you need a bit more thought on this. How do you propose the studio/flat to be completely electrically seperate if the cut out (such as it is) is in an adjacent house and would require access to it in case of fault? How is metering proposed to be done?
I've not even thought of the garage supply yet, is that supposed to be on with the house? Or is that another independent supply?
Honestly, back to the drawing board for you
:)
Possibly not explained very well. 1 Ph intake / meter at house. Meter covers house, studio flat and garage. By electrically separate what I meant was, if a RCD operated in the flat, the tenant could reset it locally within the flat as opposed a RCd sited in the garage. Hope the helps
 
So an MCB feeding and RCD in the flat feeding an RCD in the garage?
See earlier comment mate. I'm sorry but I'm just not getting how you're proposing to do this. There are much easier ways imo.
Garage on the downstairs RFC thus eliminating the need for any switchgear there. What are you going to need in there? A light and a socket, piece of cake man.
Tails into henleys in the house and split off to flat, seperate fuse up there and a landlord's meter there to allow for recharging of energy used at an agreed rate. RCBO CU in the flat, jobs a goodun
 
Last edited by a moderator:
So an MCB feeding and RCD in the flat feeding an RCD in the garage?
See earlier comment mate. I'm sorry but I'm just not getting how you're proposing to do this. There are much easier ways imo.
Garage on the downstairs RFC thus eliminating the need for any switchgear there. What are you going to need in there? A light and a socket, piece of cake man.
Tails into henleys in the house and split off to flat, seperate fuse up there and a landlord's meter there to allow for recharging of energy used at an agreed rate. RCBO CU in the flat, jobs a goodun
Thats exactly what I don't want Trev. I don't want a flat RCD feeding garage RCD

SWA was installed for garage and possible office above. After house 1st fixed, owner decided to make the office a studio flat to rent out.
 
I may well do that in the end Murdoch......The house is 22 x RCBO's + 1 x MCB for garage / studio flat. Studio flat may have approx 5 circuits inc smoke /heat. Garage approx 2/3 circuits

FFS can't you spell!

If you've used RCBO's in the house then using them in the studio makes sense. Garage could be 1 RCBO and 1 MCB
 

Reply to New build, garage, studio flat above. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
786
Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
588

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top