New build outside light | Page 5 | on ElectriciansForums

Discuss New build outside light in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 12, 2011
Messages
191
Reaction score
32
Location
Ayr
Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
 
Id like to add that a cpc is not there to protect the cable neither is it needed for fault protection on a cable. Its there to connect 'exposed' conductive parts to earth. Last time i checked 25mm tails they didn't have a cpc within them. You get plenty of class 2 appliances with 2 core flex. I guess they forgot the earths. I agree its not good practice, but in the real world to a class 2 fitting.........
 
My, my, 100 replies and I,ve(the OP) not got a definitive answer. Glad I,m now retired.
Well at least this thread will give you something to read to pass the time :(
 
Thanks gents, just wonder now if my son can push Bellway(the builder) to run an earth to the light fitting. The house is 15 months old
The cable more than likely has a cpc, it's probably been chopped off by the "Electrician" that fitted it, soley because it is a class 2 fitting and the cpc was nothing more than a nuisance to him, isn't knowledge in something you know little about a wonderful thing?
 
Thanks gents, just wonder now if my son can push Bellway(the builder) to run an earth to the light fitting. The house is 15 months old
The cable more than likely has a cpc, it's probably been chopped off by the "Electrician" that fitted it, solely because it is a class 2 fitting and the cpc was nothing more than a nuisance to him, isn't knowledge in something you know little about a wonderful thing?
 
To say that double or reinforced insulation is not allowed in a domestic installation is incorrect.
Virtually every installation uses double insulation (call it insulated and sheathed if you will) at the origin, i.e. the tails.
Then of course there’s the flexes used in pendants, the double insulated light fittings and extractor fans.
What is not allowed, is an installation which is entirely double insulated.

Certain there have been a number of threads regarding the provision of a CPC at every point and accessory in a wiring system.
As such, I don’t understand why there is any confusion about this?
Yes it is required, except at lampholders having no exposed-conductive parts and suspended from a point which does have a CPC (most people also apply this to other lampholders which are not suspended, such as down lights).

As for the OP, there should either be a CPC present at the light fitting, or at the least, a nearby junction box.
You may find there is sufficient slack in the cable to cut back the outer sheath and still be able to terminate the CPC and live conductors in the new fitting.
 
Last edited by a moderator:
To say that double or reinforced insulation is not allowed in a domestic installation is incorrect.
Virtually every installation uses double insulation (call it insulated and sheathed if you will) at the origin, i.e. the tails.
Then of course there’s the flexes used in pendants, the double insulated light fittings and extractor fans.
What is not allowed, is an installation which is entirely double insulated.

Certain there have been a number of threads regarding the provision of a CPC at every point and accessory in a wiring system.
As such, I don’t understand why there is any confusion about this?
Yes it is required, except at lampholders having no exposed-conductive parts and suspended from a point which does have a CPC (most people also apply this to other lampholders which are not suspended, such as down lights).

As for the OP, there should either be a CPC present at the light fitting, or at the least, a nearby junction box.
You may find there is sufficient slack in the cable to cut back the outer sheath and still be able to terminate the CPC and live conductors in the new fitting.
Common domestic electric cable types used in the UK - https://www.diydata.com/materials/electric_cable/electric_cable.php
See the explanation below 3 core and earth cable, in the link provided, pretty much sums the debate up.
 
To say that double or reinforced insulation is not allowed in a domestic installation is incorrect.
Virtually every installation uses double insulation (call it insulated and sheathed if you will) at the origin, i.e. the tails.
Then of course there’s the flexes used in pendants, the double insulated light fittings and extractor fans.
What is not allowed, is an installation which is entirely double insulated.

Certain there have been a number of threads regarding the provision of a CPC at every point and accessory in a wiring system.
As such, I don’t understand why there is any confusion about this?
Yes it is required, except at lampholders having no exposed-conductive parts and suspended from a point which does have a CPC (most people also apply this to other lampholders which are not suspended, such as down lights).

As for the OP, there should either be a CPC present at the light fitting, or at the least, a nearby junction box.
You may find there is sufficient slack in the cable to cut back the outer sheath and still be able to terminate the CPC and live conductors in the new fitting.
The protective measure double or reinforced insulation is only applicable
to electrical installations or circuits that are under effective supervision in normal use to ensure that no change is made that would impair the effectiveness of the protective measure.
I do not think domestic allows for this.
Despite there possibly being class 2 equipment used in the installation inevitably your primary protection against electric shock to the lightning circuit will be ADS.

The crux of the matter is that if anyone wishes to change the light to a metallic one in construction then there pretty much out of luck.
 
Last edited:
[ElectriciansForums.net] New build outside light
Pretty much sums it up
 
The protective measure double or reinforced insulation is only applicable
to electrical installations or circuits that are under effective supervision in normal use to ensure that no change is made that would impair the effectiveness of the protective measure.
I do not think domestic allows for this.
Despite there possibly being class 2 equipment used in the installation inevitably your primary protection against electric shock to the lightning circuit will be ADS.

The crux of the matter is that if anyone wishes to change the light to a metallic one in construction then there pretty much out of luck.
"There pretty much out of luck" Good professional, best practice, no use to anyone, advice.
 
"There pretty much out of luck" Good professional, best practice, no use to anyone, advice.
It’s not advice, it’s what the reality is when people just cut out the cpc at a item of equipment such as a luminarie.
I’ve stated numerous times that it’s poor practice ( have you actually been reading the replies?), so go do something about it then if it’s a new install.
 
Last edited:
It’s not advice, it’s what the reality is when people just cut out the cpc at a item of equipment such as a luminarie.
I’ve stated numerous times that it’s poor practice ( have you actually been reading the replies?), so go do something about it then if it’s a new install.
Apologies, did not read your post properly. Sorry
 

Reply to New build outside light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Good luck with your project and I’m starting in 2 weeks to install the same thing as you.
Replies
3
Views
767
  • Question
Some pir lights have a switched output so you can link them together, when any pir is activated then all lights will come on. if you don’t connect...
Replies
1
Views
897
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
Replies
21
Views
989
nicebutdim
N
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks