Hi guys been more of an observer than a poster but need some answers if anyone can help so here it is.
i have picked up some work on a couple of new builds that were started before the recession the original sparks have went bust so im told any way i have been asked to finish the job but there are a couple things that concern me.
1 The meter box is outside on the wall and they have brought a split concentric in to the consumer unit > 3 metres
also it is not > 50mm below the surface can i fit an s type rcd from the meter to then feed a kmf.
2 The family bathroom has a 240 v fan cored through the wall in zone 1 above bath is there i think it about 2mtrs from floor but not if your standing in the bath is this okay i have a feeling that fans were okay as long as it was above a certain height in zone 1 thanks to all in advance