Agree the non trip would indicate a duff RCD the other faults you mention, I'm not so sure.
As stated, it was definitely the RCD. Once changed, all faults were cleared. Have reported it to MK and they are aware of the problem.
 
I came across a L an N reversals only a few months ago.
Was called out to a kitchen circuit tripping... found a screw in the wall and into the cable. But as part of the testing I noticed the L and N were reversed in the entire house.
On close inspection I found the incoming feed had been reversed by the electrician who had connected the solar panels some months ago. I rang the company and sent them some pictures. They said they used a local electrician as theirs was too busy and as such can't accept responsibility. I reported them to local building control....I heard nothing.
 
I came across a L an N reversals only a few months ago.
Was called out to a kitchen circuit tripping... found a screw in the wall and into the cable. But as part of the testing I noticed the L and N were reversed in the entire house.
On close inspection I found the incoming feed had been reversed by the electrician who had connected the solar panels some months ago. I rang the company and sent them some pictures. They said they used a local electrician as theirs was too busy and as such can't accept responsibility. I reported them to local building control....I heard nothing.

Please tell me YOU fixed the problem as a matter of priority?
 
Lol.
Loving the tongue in cheek sarcasm.
The best of it was, I billed the solar panel company a,silly amount and they paid it within two days. Based on how long it took and what they paid, I was on par with yaya toure in terms of wages.
 

Reply to New Consumer Unit Installation - L&N Reverse at the sockets in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
The 0.05 ohms comes from the OSG, I have not seen it in the regs book. Certainly if the readings obtained were for intial verification tests as...
Replies
2
Views
722
OLDBOY
O

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top