Hi
I have been asked to quote for some remedial and extra works such as new gas bonding,new circuit for boiler supply,light and switch in loft,2 extra sockets in kitchen,shaver point in bathroom and change some socket and switch plates.
The customer had a EICR done about a year ago which was classed as unsatisfactory.
One of the faults was the entry hole for the tails being too big and that the tails being 16mm were too small.
The customer wants a certificate to say its all satisfactory when the work is all done.
I will be issuing a new EIC for the boiler circuit and minor works certs for the additional works.
Should I instead recommend a board change and EIC then the whole installation would be covered.
Ive attached a pic of the existing consumer unit,RCD 30ma from the 1980s I think.
Any views would be much appreciated.

[ElectriciansForums.net] New Consumer Unit,what do you think ?
 
A C2 maybe, if was my job I would quote for the work that has been requested, and a new EICR afterwards, you could try and get RCBOs fitted and change the RCD for a Main Switch, but looking at the pics, that avenue may not be possible, if the hole for the tails is the only issue fit one of the tail entry glands.

No an eicr has been done and a report produced and paid for by the customer. All you need to do is produced an EIC with all jobs youve completed in section "extent of work covered by this certificate" and cross refrence the report number of the eicr already done. A headed letter attached is also advisable explaining this but not always necessary.

No customer will want to pay for retesting circuits that have allready had the all clear!!
 

Reply to New Consumer Unit,what do you think ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top