New 46kVA electric supply to new backland dwelling (37m from footpath). Mains cable runs along the footpath at the road access.
Which option would you choose and why?

Option 1

Meter box near footpath. Own fuse and armoured cable (>30m distance) underground to new dwelling.

Option 2

Meter box 25 m from footpath. Own fuse and armoured cable (<15m distance) underground to new dwelling.
 
46kVA to a dwelling?? Are you sure you actually mean that?
 
With respect, I think you need to take a second look at your demand calculations. Post up exactly what it is that you’re looking at building.
 
With respect, I think you need to take a second look at your demand calculations. Post up exactly what it is that you’re looking at building.
One dwelling
with up to 2 EV chargers
22kW fast x 2
43-50kW rapid x 1

Charging point can be located near external meter box if needed to simplify cable to dwelling

Trying to understand pros and cons of external meter box located near mains cable OR nearer to dwelling
 
I'm assuming that you've already had the DNO quotation for the new transformer, etc etc?
 
In the meantime, to answer your question, you want to get the DNO intake and meter as close to the property as possible - the simple reason being that as/if/when something goes wrong it's the DNO's responsibility to fix it, not yours!! Remember - you only own from the meter onwards.
 
From your pic, I'd strongly suggest you just get the DNO to quote for a new supply to the property. And if you really DO want that much energy, I'd just ask to get a 100/3ph installed instead - may well be cheaper and will certainly be safer and easier to deal with on site.
 
In the meantime, to answer your question, you want to get the DNO intake and meter as close to the property as possible - the simple reason being that as/if/when something goes wrong it's the DNO's responsibility to fix it, not yours!! Remember - you only own from the meter onwards.
Great. Understood, thanks
 
You mean three phase?
If the DNO are talking two phase (230-0-230) then 3 phase may not be available. This has been a problem throughout most of my working area. Quite a few of my customers have two phase supplies, including myself, but I can count the number of customers I have with 3 phase supplies on the finger of my hands. Possibly just one hand.
In answer to the OPs question, definitely not option 1.
 
agree with 3 phase option. you might want 3 phase equipment at some time in the future. and meter box as close to the dwelling as possible.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

wwilts

DIY
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
New electric supply connection
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38
Unsolved
--

Advert

Thread statistics

Created
wwilts,
Last reply from
Gavin John Hyde,
Replies
38
Views
3,611

Advert

Back
Top