Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final.
1) In part 2 of the AMD2 small works cert, its wants Zdb supplying the final circuit. Does this mean the Zs for the ring final that I measure or the MaxZs 32A MCB which is 1.1?
2) for part 3 of the cert, is the new FCU 13A then in effect the new DB and therefore I would put in FCU, BS 1362, 13A?
3) Then for part 4 test results do I complete the R1+R2 just for the cable from the new socket to the FCU? will my max Zs be the rating for the 1362 fuse at 1.83?
Thanks for your help,
gordon daly
1) In part 2 of the AMD2 small works cert, its wants Zdb supplying the final circuit. Does this mean the Zs for the ring final that I measure or the MaxZs 32A MCB which is 1.1?
2) for part 3 of the cert, is the new FCU 13A then in effect the new DB and therefore I would put in FCU, BS 1362, 13A?
3) Then for part 4 test results do I complete the R1+R2 just for the cable from the new socket to the FCU? will my max Zs be the rating for the 1362 fuse at 1.83?
Thanks for your help,
gordon daly