S

solgen

Hi,

I've recently run 4mm 4 core SWA from a 20A MCB house consumer unit to a garage unit installed in a shed 50M away. The garage unit has 16A and 6A breakers protected by 40A 30mA RCD main switch. All wiring connections seem to be correct, however, as soon as anything is placed under load either from socket or light, the RCD back at the house consumer unit trips. I have visually inspected everthing so far and cannot see any problems.

I looked for neutral problems and cannot see anything amiss.

Can anyone suggest where the problem maybe?

Thanks
 
I would imagine, that the RCD tripping indicates there is a fault.
It could conceivably be due to an accumulation of earth leakage from a number of circuits being protected by the RCD at the house.
Have you tried switching off the other circuits and then switching on a load in the shed?
 
Most common thing i find with shed installs is water getting into the fittings somewhere, we've had a lot of rain recently and if its just started happening - this is where, if i were you, id probably start looking first.

Spiderman onto the shed roof and see if the felt / tiles (whatever it is) are knocking on death's door.

As above, IR test.
 
I've seen it numerous times. Everything seems fine - IR all circuits, all +100m, then only when you connect a load the supply RCD trips.
As the neutral current is not returned to the sub circuit RCD it throws it out of balance and trips.
 
As the RCD will constantly monitor P-E and N-E faults in no load conditions I would say it's highly likely to be a wrongly connected supply neutral but you are right, there maybe circumstances where it could be something else.

Solgen any chance of a picture of the CCU?
 

Reply to New shed circuit tripping RCD at house consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top